An oil production facility is concerned about spacing of hazards prone to detonation. What would be the distance from a 181 lb TNT equivalent vessel explosion that failure of concrete block walls would occur? a. 154 ft. b. 200 ft. c. 244 ft. d. 317 ft. Solution | Posted 07/26/18
5 Comments
FPE
7/25/2018 09:05:12 am
b. 200 ft.
Reply
Colleen
7/25/2018 10:18:36 am
I got A. 154 ft
Reply
Jimmy
7/25/2018 11:53:56 am
Damn, I learned something: we are given lbs of TNT, not kg. Also, note the example in the FPH says double the blast wave energy when you use Table 2.8.1. So, if by chance you forget to convert to kg, AND forget to multiply by two, you get 158, which happens to be really close to 153.3 (if you do it correctly on your EIGHTH try, um, like I finally realized) which is most nearly 154. What are the odds the real exam will be so forgiving? Pay attention to simple errors that you tend to repeat--I blow units REGULARLY.
Reply
Colleen
7/25/2018 12:01:27 pm
Better to mess up now than on the real exam!
Reply
Pari
7/26/2018 12:06:55 am
200
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |