We have an exit enclosure that is rated as Class I Division I. My understanding of an accessible route and means of egress, is that it is a "safe" means of egress.
Can an accessible route have a Class I Division I (explosion hazardous classification), or does it need to be purged and pressurized according to Type X requirements? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
This week is the third of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here. The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
We have a fire pump room which is very constrained.
NFPA 20 (Edition 2016), A.4.21.1.2 (2) For horizontal split-case fire pumps, there should be a distance of not less than 10 diameters of suction pipe for side connection (not recommended) to the fire pump suction flange. The main pumps have a capacity of 3000 gpm (two are electrically-driven and two are diesel-driven) with two jockey pumps at 300 gpm capacity. All are in one room. Pumps suction and discharge pipe size is 12" as per Table 4.27 (a). In this scenario, what is the meaning of 10 diameters - is it 10 times of suction size diameter of pump (means 10x12= 120") or something else? Why is this requirement only limited to suction and why not for discharge side as there is tapping for pressure monitoring? Any thought would be much appreciated. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe I’m a Fire Inspector/Design Reviewer and I have a problem that I’ve been trying to tackle. NFPA 14 systems are designed for high volume low pressure firefighting tactics, but the majority of fire departments in America use high pressure low volume equipment. Here are the key points:
NFPA 14 Type 1 standpipe systems provide 250 gpm at 100 psi with 200 ft to most remote location in a sprinkled building. In the firefighting world this equates to a fire attack with 250 ft of 2.5” hose and a 1-1/8” smooth bore nozzle. The 250 ft comes from, 50 ft to stretch to the hose connection on the floor below the fire floor and 200 ft to most remote location on the fire floor. Fire ground friction loss calculations for 250 gpm through 2.5” hose is 15 psi loss per 100 ft. A smooth bore nozzle requires 50 psi to operate properly. We are stretching from the floor below so we have roughly 6 psi head loss. So the required pressure at the hose valve is 93.5 psi. You can see that the NFPA 14 design requirements are in line with the use of this higher volume lower pressure equipment. The problem is that 2.5” hose is very heavy and requires a lot of man power. 2.5” attach lines are used by large city departments like Seattle, New York, and Chicago. Many smaller city and town departments don’t have the staffing to stretch such big lines. We may only have a couple firefighters stretching an attack line where as the big cities would have 6 or more. So we use smaller more maneuverable hose and more pressure demanding fog nozzles. A more typical firefighting set up in the majority of fire departments would be 1.75” or 2” hose and a 75 psi or 100 psi fog nozzle flowing between 150-200 gpm. I’ll use Bozeman as an example. We use 1.75” hose, a 75 psi fog nozzle, and a target flow of 175 gpm. In our experience the pressure loss per 100-ft of 1.75” hose with 175 gpm is 50 psi. So if we need to stretch 250 ft of hose, we would need 206 psi at the hose valve on the landing below the fire floor. Add in that the tallest building we have is 11 stories, and a 25 psi pressure loss adjustment for pumping the FDC, and we are up to 285 psi required at the FDC. There seems to be a disconnect between the design world and the firefighting world. This poses all sorts of problems such as compromising sprinkler systems and old standpipe systems since they may have components that are not rated for such high pressures. Even worse are systems with pressure reducing hose valves that wouldn’t even allow us to pump the FDC to get anywhere near the pressures we need with our equipment (see One Meridian Plaza fire in Philadelphia). I think that Fire Departments need to communicate their design needs to designers, and Fire Departments also need to look at the equipment they use, and see how they can make changes to operate more closely to what NFPA 14 systems are designed for. If you have any knowledge on this topic I would love to hear it, thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Does anyone have any pressure maintenance pumps installed on their sprinkler systems without having a fire pump?
In other words, having a pump on the sprinkler system that is only there for the purposes of preventing a false alarm (due to pressure ebbs and spikes in the water supply) instead of boosting the water pressure like a traditional fire and jockey pump combination. We have some legacy jockey pumps installed like this and it runs into a grey area for maintenance as they don't affect the performance of the sprinkler system they are connected to. Any thoughts? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe We are pressure testing a sprinkler system but there is no water available.
How much air pressure should be used to equal a 200 psi hydro test? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Design criteria for storage occupancies have changed substantially over the years from pipe schedules to the NFPA 231's to NFPA 13, 2016. Everyone talks about "grandfathering" old system designs, but no one can ever point out any specific codes, standards, or formal documents that give any solid guidance on this matter.
In our state, this situation varies by jurisdiction, but the opinions are all over the place and usually wind up at the classic "ask the AHJ". This is very time consuming and often times not very helpful since most of them enforce the newest NFPA editions when unless you can provide as-built documentation which we can't do 95% of the time for old buildings. We all know that it depends on the situation, but there has to be some level of formalized consistency out there to start with. As a NICET certified Fire sprinkler designer, I have my own professional opinions on the matter based on my understanding of the intent of grandfathering and my own project experiences. That said, can anyone point me to specific codes, standards, or formal documents that I can utilize to create a formalized opinion that can be submitted to local AHJ's for a more "standardized" understanding? I'm pretty well versed in NFPA 13 so I'm really looking for IBC, NFPA 101, NFPA 1 references, but all feedback is appreciated. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Anyone familiar with the historic tax credit requirements in Massachusetts regarding minimum distance of mechanical systems from the windows?
We are being asked to keep all pipe and heads a minimum of 3'-0" from exterior windows. Not a huge issue for installation, we're just curious where this is stated. We haven't been successful in getting this information from the A&E team. Any ideas? Thank you. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe This week is the third of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here. The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
I'm working within a campus environment, and costs are something that always arise at some point during ITM conversations.
Does anyone have a great resource or tool to help to estimate a ballpark cost of ITM over a life of the building? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Does the 'small room rule' apply to NFPA 13D sprinkler systems?
I could not find any mention of it in 13D. If 13D does not allow it, why not? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe While working on a sprinkler project I came across a Spiral Freezer. It is a conveyor system. Rendering of a two-level Spiral Freezer Conveyor System. I am mostly interested in how it needs to be protected. At this time I see two and neither have protection within the Freezers. This facility is not new, but I know they are upgrading the fire protection throughout.
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I’m confused by the field of view intent of NFPA 72 for synchronization.
Do two adjacent rooms with a door between them each with strobe coverage require synchronization? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Is there something where I can input fire pump test results and create a fire pump curve that I can print off and include with fire pump testing results? Possibly something I can input our company name on as well? Thanks in advance.
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe This week is the second of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here. The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here. Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
We have a long, narrow basement space which will be used for storage. Because of the direction of the structure, we plan to cover the long but narrow space by two branch lines with 8 sprinklers on each line. When we're trying to determine the remote area, NFPA 13 says that the minimum length along the branch line must be 1.2 x √(remote area), which for us is 2,000 sqft. This comes out to a minimum of six sprinklers. However, if we have two branch lines with six sprinklers each, we only reach 1,560 sqft.
Is there a maximum number of sprinklers that is required to be calculated along a branch line, or for narrow spaces does the design area just take a very long and narrow coverage until it reaches the required size, regardless of how it lays against the branch lines? Thanks in advance! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Please can someone give some information regarding the filling speed of a empty pipeline to a sprinkler line?
In my case there was water hammer in a 6” line, The 16” firewater line was under 175 psi pressure and the opening time was 9 seconds. Is 3 feet per second more realistic? Or is there a NFPA standard that addresses this? Thanks in advance for your support! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I am working on a project with male and female restrooms in separate structures located near a park. The structures are roughly 500 sqft. The structures must comply with NFPA 101 for means of egress. I am trying to figure out travel distance requirements.
What occupancy would you classify the restrooms as? And in turn what would be the maximum travel distance if there is only a single door? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Anyone have experience with fire protection for a vehicle bridge?
I must review NFPA 502 but I wanted practical experience, too. The project information I have is minimal at this point, but I looked in NFPA 502 and assume some kind of dry pipe system to supply hydrants and potentially sprinklers on the bridge would be necessary at this point. Just looking for some guidance based on past experience. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Are isolation valves allowed to be installed after dry valve for a standpipe system?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe This week is the first of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here. The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. See the entire scoreboard here. Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. Every week of the series is retroactive so you can still test yourself with past week exams
I have a situation in a locker room in which the lockers themselves were built too high resulting in only a 12" clearance instead of having 18". It's a B Occupancy (IBC), light-hazard with standard-coverage QR heads (12'x12' grid).
Could we feasibly swap the heads out for extended-coverage QR heads (16'x16') and meet the intent of NFPA 8.5.6 for clearance? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Question for AHJs and inspectors:
Do you occasionally see fire alarm strobes mounted on the ceiling that appear to be for a wall-mounted orientation (e.g. they are rectangular and have the word "FIRE" on the side)? I know some of these are actually for ceiling mounted applications but I've run across some that are wall-mounted only. I think the Wheelock brand might be an example? Stuff like this is hard to tell in the field for an existing building (with no documented cut sheets for what was submitted). Anyone have tips or tricks for this? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe We're determining fire sprinkler hazard classification for a cannabis grow facility. It is under International Fire Code occupancy F-1 and I would lean to Ordinary Hazard Group II as an Agricultural facility. However, I'm concerned with 23' high racks with three level of ABS plastic pans containing the plants in the flower rooms.
Would this are be considered storage and more specifically rack storage exceeding the OH II classification? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I have a new highrise building with a water storage tank/room for the fire sprinkler system. The entire room is the storage area.
Is sprinkler coverage required for this room? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |