Is there a room volume cut off that you use for clean agent space to make sure that your system will pass the room integrity fan test?
As an extreme example, a 50,000 sf space would probably be better for something like a double interlock preaction system since it would be difficult to make sure that the space is of tight enough construction to hold the clean agent (there will inherently be some leaks in construction despite doing all the recommended practices of gasketing, door threshold blocking, etc). Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
We have a project where we're adding a sound (anechoic) chamber and and protecting it with clean agent.
A question came up as to whether or not dampers are required for the HVAC system that provide supply and return air to the pre-manufactured chamber. Is an anechoic chamber required to have dampers for limiting the migration of the clean agent? My thinking is that the clean agent will be activated by an air sampling system, so there should be no meaningful amount of smoke in the chamber. That said, do the dampers have to be listed for fire/smoke? Any help with getting specifics from code or a clearer understanding is always appreciated from the community so thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe 3M recently announced they will no longer manufacture NOVEC 1230 by end of 2025 due to the presence of PFAS (https://news.3m.com/2022-12-20-3M-to-Exit-PFAS-Manufacturing-by-the-End-of-2025).
Other similar agents, such as FM-200, have similar environmental concerns due to having HCFCs. Does anyone know a chemical fire suppression agent that doesn't have CFC or PFAS issues? I know there is a new NFPA standard (770) on hybrid systems and that the Victualic Vortex is one such system, but not sure what other alternatives are out on the market. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What are some popular solutions for elimination of wet-pipe sprinkler systems in data centers that have installed wet-pipe, VESDA and clean agent systems?
A client wants me to find a solution that will be acceptable to the local Authority Having Jurisdiction to eliminate the wet-pipe sprinkler system in the data center portion of the facility. We already have the VESDA and clean agent. Are there other recommendations/insight here that might be helpful? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Given the HFC (hydrofluorocarbon) production phase-out, what are you currently recommending to your clients and customers regarding the installation of new FM-200 systems at this time?
Just curious to get a status check on how you approach this challenge. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am working on a project that is manufacturing lithium-metal batteries (not lithium-ion). There are multiple areas throughout the manufacturing process where there is a risk of exposed lithium metal.
With lithium being water reactive, any water based system is not an option. Are there any known alternative fire suppression systems listed and approved for use on a lithium fire? I know that per a couple of different NFPA codes that clean agent and dry-chemical systems are not recommended for use on lithium fires. From what I can find there are just manual fire extinguishers (such and ANSUL's lith-x) for use on lithium fires. Any input would be greatly appreciated. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We are designing a clean agent system for electrical rooms located within a high-rise building. We are proposing having dedicated clean agent releasing control panels for the electrical rooms, and a separate building Fire Alarm Control Panel.
Is it mandatory to connect fire/smoke dampers (and other shutdown devices) in the electrical room with the clean agent releasing panel, or can these be connected to the building fire alarm system? Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe Our common CRAC Units (Cooling, Refrigeration and A/C) for data centers only cool the air directly from the data center and back into the data center.
Do these need to be shutdown with the use of a total-flooding clean agent system? If the CRAC unit is only exchanging air within the same space then I'm not sure what harm it would do if it's running during or after clean agent discharge. I'm curious if I'm off the mark here, thanks! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe NFPA 2001 requires a safety factor under sections 5.4.2.3 through 5.4.2.5 for clean agent extinguishing concentrations.
What is the difference between the "design concentration" listed in Table A.5.4.2.2(b) (2015 edition) and this minimum extinguishing concentration (the minimum extinguishing concentration MEC x applied safety factor)? In some cases the design concentrations are higher than the MEC x safety factor - is there a proper one to be using under NFPA 2001? Sorry if the question is basic - I've always just used the design concentrations. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |