Is there a possible error in the definition of a "Cryogenic Fluid"?
The IFC, NFPA 400, and NFPA 55 all define a cryogenic fluid as "A fluid having a boiling point lower than -130°F at 14.7 pounds per square inch atmosphere (psia) (an absolute pressure of 101.3 kPa)." Following that exact wording of this definition, virtually every gas would be considered a Cryogenic Fluid. Fluids, while not defined by any codes, are either gases or liquids. The air we breathe has a boiling point of -317°F at 14.7 psia. Air is a fluid. Clearly, this is not the intent of the ICC or NFPA. The NFPA Handbook indicates that a cryogenic is a liquified gas kept below 130°F. The definition should be changed to "a liquid having a boiling point under...." from "a fluid having a boiling point under...." Have any fire protection professionals ran across a situation like this where the strict definition was incorrect? How did you handle it? I am considering just making a paragraph in my report explaining my logic and going along with my day. Or would you not even bring this up with the AHJ because the intent is clear? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Do liquid nitrogen storage rooms need to be fire-resistance rated?
According to NFPA 55 (2016 Edition) Section 6.4.4, gas storage rooms need to be 1-hour fire rated, but it just seems odd since nitrogen can be used as an extinguishing agent. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |