I'm currently working on a project for a packaging factory in which there are rooms which are used for storage of Milk and Juice in stainless steel tanks that are about 1.5 m (4.9 ft) in diameter and 8 m (26.2 ft) in height.
There are about 5-6 tanks for each area (milk and juice storage). Each room is about 70 sq.m. (753.4 sqft). The ceiling height is about 11.1 m (36.4 ft). The content combustibility (i.e. Milk & juice) is low and the quantity is high. Since the height of the tanks is above the threshold of 3.7 m (12 ft), I cannot consider it to be protected by LH or OH1 curves and it should come under storage occupancy and commodity classes. Since my exact requirement is not present in the list of commodity classes in NFPA 13, I figured it to be Class 1 per the liquid content. Accordingly, it would be under Commodity Class 1 curve in NFPA Chapter 14 Figure 14.2.4.1 (2013 Edition) and multiplication factor for density vs storage height from Figure 14.2.4.3. Kindly let me know if I'm on the right track or if there is something which I overlooked. Note: This is a Daily Discussion question submitted anonymously to us by a Toolkit member. Discuss This Here.
2 Comments
Glenn
6/5/2018 09:30:37 am
NFPA-13 Chapter 14 is "Protection of Class I to Class IV Commodities That Are Stored Palletized, Solid Piled, Bin Boxes, Shelf Storage, or Back-to-back Shelf Storage".
Reply
Franck
6/5/2018 10:41:14 am
Fully agree with Glenn
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |