How do I properly perform hydraulic calculations for a sprinkler system with two water sources?
The system we have is supplied by two independent street mains. Each service has a slightly different static and residual pressure. The calculations need to show both supplies. Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Colin Lusher
9/25/2020 10:13:05 am
Dual water supplies are normally provided for redundancy/reliability. If that is the case, then you should pick only the weakest water supply, and perform a calculation with only the one water supply, ignoring the redundant supply.
Reply
Ivonn
9/25/2020 10:52:02 am
Agree with the comments and question of Colin Lusher
Reply
Justin Milne
9/25/2020 10:23:22 am
I have this same question!
Reply
9/25/2020 10:50:17 am
For the simplest results, calculate to the weaker of the 2 water supplies. However to properly calculate 2 water supplies you will be required to balance the flow from both until the pressure loss from both supplies to your demand system are the same or close enough (within ~0.5 psi of each other). You do this by running 2 calculations, one for each of the supply, making an assumption about the flow entering from the other supply. Compare the pressure losses and make adjustments on your initial assumptions and repeat the calculations until both calculations' pressure losses to the system are close.
Reply
Paul G
9/25/2020 11:24:10 am
This^ Better than I was trying to explain it. You can also complete your sprinkler calculations to a common point where the supplies connect to get your estimate demand for balancing.
Reply
Brian Gerdwagen FPE
9/25/2020 12:31:22 pm
I use the weaker water supply, but at both locations as if it was supplying the underground from two locations.
Reply
Franck
9/25/2020 01:03:51 pm
As indicated above, it is wise to compare to the weakest and use the second one as a back up (to avoid a water supply impairment in case of works on one water supply).
Reply
Mark H
9/25/2020 04:56:32 pm
All great comments. Only thing I have to add is if the two connections supply common site private fire hydrants you could do on site flow test and use that for your supply but I would agree with all the comments about using weakest of the two supplies and consider the second tap redundancy. Would also confirm elevation between the two tests is not a factor.
Reply
SK
9/25/2020 10:53:48 pm
In practical, required water can not be drawn from both sources, Hydraulically it'll draw water from Stronger supply if both are connected, adequate and fulfill the required demand. So if you want validate viability of your system, design/check with weaker one, and make other alternative supply, the purpose would be solve.
Reply
Franck
9/27/2020 08:22:10 am
Although it is a good practice to consider one water supply and the other as a back up, it is also true that if you have 2 water supplies, water will be delivered by both (adding the flow at the same pressure).
Reply
9/29/2020 06:22:12 pm
The method I would use to hydraulically calculate the system is to first use HYENA+ (hydraulic analysis computer software - disclosure: I own the company) to calculate the required Input Point Flow/Pressure (with one input point).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop April '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
May 2024
PE PREP SERIES |