I do inspections for fire alarm systems. It's not something that is brought up often and is generally not an issue, but I am trying to educate myself on what the correct procedure is to determine the conduit size for fire alarm.
Could someone point me in the right direction? Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments
NFPA 72 states that audibility from a fire alarm system is required to be provided throughout a building. Most jurisdictions are less concerned with attaining audibility in small, non-normally-occupied rooms such as janitor closets, small electrical rooms, or small mechanical rooms. However, several military reviews have pointed to exactly these rooms and asked how audibility is going to be achieved.
I typically provide speakers just outside of these groups of rooms such that there should be an achieved audible level, but how could I prove that during the design phase? Is there any calculation for audible loss through a door or software that could model this loss? I feel like there's a good handful of variables that play into whether audibility is achieved in these small rooms that may be difficult to predict. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe A dormitory has residential rooms which house two students. There is a traditional sleeping area approximately 12 ft x 12 ft, and a hallway with a bathroom and closet in-between the sleeping area and the main corridor.
Separating the sleeping area and the unit hallway is an opening about the size of a door opening (but with no door). This project is still in design. How shallow would the header on this opening need to be (distance from the ceiling), in order to avoid requiring a smoke detector in the sleeping area and the hallway? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I'm considering testing for NICET fire alarm certification. What I don't yet know and would be very interested in is who typically prepares fire alarm shop drawings?
Do freelance fire alarm designers/engineers make up a large portion of shop drawing preparation, or is it mostly all completed by a fire alarm company's designer? Do large manufacturers (Simplex/JCI) complete all of their own shop drawing work with in-house designers? Thanks in advance - I'm trying to get a better perspective for my career. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe A liquid storage tank rupture results in a fire containing an open 45 gallon (130 kg) tank containing animal fat. Using gross heat of combustion, estimate the time it would take to burn the remaining fuel without interruption if the tank is half filled and the fire is approximately 2.45 MW. a. 1.2 seconds b. 11 minutes c. 18 minutes d. 17.6 hours Solution | Posted 08/06/19
Which of the following would not require a fire alarm system? a. A new second-floor tenant insurance sales office of 60 people b. An existing four-story fraternity house of 70 people c. A single-story 80,000 sqft high-hazard warehouse of 90 people d. A new single-story 35,000 sqft Class A department store Solution | Posted 07/31/19
Which of the following is not a preferred interface between fire alarm and smoke control systems due to the requirement for equipment to be listed as compatible? a. Equipment connected to Building Automation/Management System, which is connected to Fire Alarm by network connection b. Equipment connected to Building Automation/Management System, which is connected to Fire Alarm by electrical contact/relays c. Digital Control Equipment connected directly to Fire Alarm System via network connection d. Mechanical Equipment connected directly to Fire Alarm System via contacts/relays Solution | Posted 07/19/19
A forensic investigator is trying to determine approximate timing of events after a fire within a hospital basement. A quick response sprinkler (RTI of 50 m^1/2s^1/2), Ordinary Temperature (65 deg C) was within a room (2.1 m high ceiling) that has an initial temperature of 73 deg F and was exposed to a ceiling plume at 205 deg F traveling at 1.3 m/s. Approximately how long should it have taken the sprinkler to activate? a. 2 s b. 16 s c. 33 s d. 38 s Solution | Posted 07/16/19
What governs the minimum conduit size for fire alarm circuitry?
Is it just based on the ampacity factors in the National Electrical Code similar to any power circuits, or is there some other section I should be referencing from NFPA 72 or the NEC? Any help is greatly appreciated. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe A fire alarm system containing horn/strobes, manual pull stations, fire sprinkler monitoring, and heat detectors would be considered what type of fire alarm system? a. manual, temporal-3 b. manual and automatic, temporal-3 c. manual, emergency voice/alarm communication d. manual and automatic, emergency voice/alarm communication Solution | Posted 07/01/19
Do you often come across AHJs who require manual pull stations at every exit, regardless of the occupancy and regardless of whether they're allowed to be omitted based on a fully-sprinklered building?
I've come across it a few times and we certainly see some ordinances written in - I'm just curious if it's something you have seen and whether you choose to fight it or just include the pull stations. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Someone had asked about life safety Revit families and any recommendations. We do fire alarm design and are increasingly seeing BIM become the standard when working with architects.
Does anyone have any recommendations on where to find quality fire alarm Revit families? We're not manufacturer-specific design but are looking to improve our older basic devices. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe I've taken technical writing courses and have experience working with MasterSpec, US Military specifications, vendor specifications, and various ownership standard specifications.
I'm giving an internal training to our younger staff and I'm particularly interested in opinions from contractors and vendors who regularly read a variety of specifications for bidding. What advice would you give for those who write specifications? I'd be interested in helping train our staff as well as improve myself. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe We have a project where a control module is connected to the mechanical controls that is programmed to the variable frequency drive for a fan on a large unit. When a duct detector senses smoke, the control module (which is normally-open circuit) will close the circuit, sending a signal to the mechanical controls which shuts down the unit.
On this project we had a bad set of control modules that didn't work. We discovered this in testing with the local jurisdiction, and swapped out the modules and the system now works correctly. Both the jurisdiction and I wondered whether this normally-open arrangement is acceptable. If a control module were to fail, the duct detector would not be able to close the circuit on the module and the fan would remain running. In this scenario, there would be no supervision or way to know that the control module failed other than someone standing at the fan or finding the issue during testing. My inclination is that in the future these modules could be normally-closed and open upon duct detection. That way if the module fails and opens on its own, the unit will shutdown in a "failure" mode. Is it code required that this arrangement be fail-safe? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe We have a machine room-less elevator where the motor is located on top of the elevator cab and the elevator equipment is located within the elevator shaft.
NFPA 13 (2016) 8.15.5.3(2) allows sprinklers to be omitted from the hoistway of "traction elevators" where the hoistway is "protected by smoke detectors, or other automatic fire detection installed in accordance with NFPA 72", and several other requirements. NFPA 72 (2016) 21.3.3 states that only the elevator hoistway and elevator lobby smoke detectors or other automatic fire detection (as permitted by 21.3.9) shall be used to initiate Phase I Emergency Recall Operation. NFPA 72 (2016) 21.3.9 states that if "ambient conditions prohibit installation of automatic smoke detection" that other automatic fire detection initiating devices shall be permitted. What type of ambient condition in an elevator shaft would qualify as prohibiting smoke detection? I understand smoke detectors in elevator hoistways can cause nuisance alarms (NFPA 72 2016 A.21.3.9) and are very difficult to test and replace within elevator shafts, so in my opinion a heat detector would be better for elevator recall in the shaft if it's allowed by code. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe Does anyone have a good resource for determining audibility loss (dB loss) through various door types? I recall seeing a reference chart that was perhaps printed in a fire alarm handbook in the 90's, but I don't have a copy.
Intelligibility is a world all on it's own - if we need intelligibility I typically locate a speaker on the opposite side of closed doors (private offices, for instance). Is there a way I can model or predict intelligibility through closed doors? I've tried Ease EVAC years ago using door gaps, but it wasn't well suited to model the losses at that time. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe I work for an engineering consultant and we often do work directly with university and healthcare clients that expect an estimate as part of the deliverable package.
I typically track square footage costs whenever I receive them (on past projects), but even that is rare. I've since transitioned to using RS Means unit cost pricing and adjusting for location and historical cost increases. For others doing cost estimation, have you found relative accuracy using RS Means? Are there other estimating providers that are better suited for cost estimating in our industry? Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe Other than the Contractor's Material and Test Certificate for Aboveground Piping (NFPA 13) and System Record of Completion (NFPA 72), where can I find a good procedures for acceptance testing for fire sprinkler and fire alarm systems?
Is there a step by step approach that I can add to for my particular project? Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe A middle school is being expanded by two classrooms and about six small offices and supports spaces. The addition is separated by a fire barrier from the main school, and the existing school has a temporal-3 horn/strobe fire alarm system throughout (and is fully-sprinklered).
Current code requires an emergency voice/alarm communication system for the expansion, which the design team intends to provide. The question is how to address the interaction between the new voice system and the existing? Is this purely and AHJ call? Ideally, the school should consider upgrading their entire fire alarm system to voice for a cohesive message and best benefit. However, funding is very tight and we're not confident they'll have the support they need to do a full upgrade at this time. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe We occasionally have inadvertent fire alarm activations that we can't get to stop until a fire alarm company arrives to correct the issue at the facility where I work. Are we permitted to turn off the alarm and conduct a fire watch during this time instead?
Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe Can a municipal property - such as a fire station in this instance - have it's fire alarm system directly monitored by their own call dispatch center?
Posted anonymously by a member for discussion. Discuss this | Subscribe For those who regularly bid and/or review "performance-specification" or "delegated-design" drawings, what important pieces of information are often left out?
In other words, what should engineers always include for you to price or review a job effectively that you often don't get? Posted anonymously by a member for discussion. Discuss this | Subscribe A building which has an old fire alarm system is going to have its interior completely gutted (all systems, walls, everything but the structure and exterior walls are to be removed). The fire alarm system is to be demolished and replaced entirely, and the building will change to a business occupancy once complete.
Is a fire alarm system required by code to be active during the renovation? Posted anonymously by a member for discussion. Discuss this | Subscribe. Daily Discussion question submitted from a member:
I wanted to see if you have heard of any great programs, apps, databases, etc. that are appropriate for creating and maintaining panel schedules. We currently use Microsoft Access to collect data and turn it into easy to understand panel schedules for the other fire protection engineers and the maintenance team. Our panel schedules contain info such as how to impair a building (which switch’s to enable/disable), building contact info, a list of all devices and modules, info on all NACs and Power Supplies, sprinkler components and their corresponding alarm device. Microsoft Access is becoming increasingly difficult to maintain and it appears that this program has been put on the back burner for Microsoft. Have you heard about programs that other sites/companies are using? With iPad integration? With the ability to limit who can actually edit the data? Thanks for the help. Discuss this topic here. Daily Discussion question submitted from a member:
It seems that I must have missed something in the 23 years I've been in Code Enforcement. Since when has it been required for a smoke detector to be in the pit of the elevator? This is absolutely insane. We've had more nuisance alarms recently in new buildings. One is a 4 story nursing home, that the alarm has gone off 4 times. The alarm company changed the detector and it been good now. However there is still dirt, moisture, humidity, etc. All the things that smoke detectors don’t like. I've looked and Googled it and have only come up with a heat detector within 24" of the sprinkler head, which I understand. I know smoke rises so why isn't the top of the shaft sufficient? I feel we are going backwards. Discuss this topic here. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |