A middle school is being expanded by two classrooms and about six small offices and supports spaces. The addition is separated by a fire barrier from the main school, and the existing school has a temporal-3 horn/strobe fire alarm system throughout (and is fully-sprinklered).
Current code requires an emergency voice/alarm communication system for the expansion, which the design team intends to provide. The question is how to address the interaction between the new voice system and the existing? Is this purely and AHJ call? Ideally, the school should consider upgrading their entire fire alarm system to voice for a cohesive message and best benefit. However, funding is very tight and we're not confident they'll have the support they need to do a full upgrade at this time. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
3 Comments
PETE
3/25/2019 10:22:32 am
How old is the existing? If it is old enough, you may be able to make the point that you cannot accomplish strobe synchronization using new and old devices. This is mandated in 72, and it's an ADA requirement.
Reply
Raul Vasquez
3/25/2019 10:54:17 am
Unless you see two or more in line of sight, sync would not be the greatest issue nor integration. the issue is conflicting evacuation tones and or vocal messages. the old horns may be mechanical steady, march time, California, there could be electro mech, temporal 3 and the voice system could be programmed to play the same through the speakers utilizing a digital sound clip to match, but you cant offer voice evac to one side and not the other
Reply
Jason Lupa, PE
4/29/2022 09:01:14 am
Current code requires an emergency voice/alarm communication system for K-12 schools. Since the renovations will be done in phases, there will be a period with new and existing notification appliances. Speakers should be installed for the new work, but initially programmed to broadcast a NFPA 72 Temporal-3 tone to match the non-renovated areas with Temporal-3 horns. Once the entire project has been upgraded to voice, the speakers can be reprogrammed to broadcast voice messages.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |