Four-story office building wants to shut down five large air handlers nightly. Purpose is to lower energy costs when building is unoccupied. This will cause all fire/smoke dampers (FSDs) to close (the smoke detectors in return ducts need minimum operational air velocity).
The FSDs are mostly original from 1985-1988. Only UL tested for 5000 cycles and no dynamic. I cannot find a code reference to prohibit this and believe that the FSDs are already near the end of their functional lifespan. Many have been replaced due to bad actuators, binding jack shafts and missing blades. Anyone know of a code reference to prohibit this use or when a FSD must be replaced? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
[Moderator's note: since the first lithium battery question a few weeks ago, we've been flooded with more questions on the topic. We'll do our best to not overburden everyone here but still keep with the topics people are asking. As always, we're thankful for you all!]
Could anybody point out some publications that deal specifically with the ventilation of lithium-ion batteries during off-gassing and how the ventilation should be controlled? I am familiar with FM Global Loss Prevention Datasheet, and NFPA 855, and I went through some publications such as FIA, however from those I only get that there should be sufficient ventilation. I am more interested in the off-gas detection part of the design. The ventilation should be turned on and ESS turned off at the first sign of explosive gasses, but what gasses should those be? H2, CO, C2H4, CH4, or all mentioned in a combination? Not sure how to proceed in this. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For a smoke control stair pressurization system designed in accordance with IBC 909 and IMC 513, does the code require a duct smoke detector on the supply fan?
Does the installation of a smoke damper at the stairway boundary factor into this requirement? (i.e. IBC 717.3.3.2 requires a detector within 5 feet of a smoke damper). Normally this motorized smoke damper is closed and then automatically opens upon activation of a specific fire alarm signal. NFPA 92 6.4.6.2 does require a duct detector on the stair pressurization supply fan; however, I'm unaware of a similar requirement in IBC/IMC. NFPA's intent is to detect smoke on the air supply and shut down the unit before smoke compromises the stairway. For elevator hoistways that require smoke control, IBC 909.21.4.2 states to provide a detector. I would have expected a general statement in IBC 909.12 with the same intention as NFPA 92; however, I do not see a similar requirement in the IBC/IMC for stairways. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a project with a comment from the AHJ stating that the dryer vent cannot terminate to the exterior condominium wall, which is the egress wall for the condominium exit exterior breezeway on that floor.
We're under NFPA 101 (regarding Section 30-3.6.3 for Unprotected Openings). Is a duct penetration considered an unprotected opening? Dry vents cannot have fire/smoke dampers, so can it just be a metal duct? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe |