Is a two way communication system required when an elevator is installed (only for convenience) but is NOT required or designed to be part of the accessible means of egress - assuming none of the exceptions in 1009.8 apply?
Refer to CBC 1009.8: "A two-way communication system complying with Sections 1009.8.1 and 1009.8.2 shall be provided at the landing serving each elevator or bank of elevators on each accessible floor that is one or more stories above or below the level of exit discharge." Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
NFPA 72, 2016 Edition uses the phrase "2-hour fire-rated construction" in a few places; what does this refer to?
It's confusing to me since a variety of elements within the building could be 2-hour rated. For example, NFPA 72-2016 Section 24.3.13.7 states: "Two-way in-building wired emergency communication systems shall have a pathway survivability of Level 2 or Level 3. Exception: Level 1 shall be permitted where the building is less than 2-hour fire-rated construction." Buildings are not designated with a fire-rating, elements are. How do you interpret this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe While working in a MEP/FP firm, we are expanding to do projects in other states and learning to understand the different state requirements for Fire Protection / Fire Alarm.
What is the best way to go about obtaining each state's requirements for what is required in an upfront submittal? For example some states accept design drawings that only require denoting the hazard level whereas other require full design, calculations, and a written narrative. I understand and agree providing more detail is typically better; however, budgets can be significantly affected (negatively/positively) if only a hazard classification is required compared to a full design. Besides prior knowledge from working in a different state or jurisdiction, what is the best approach in determining what is required? Typically I start with searching what is required from the building code, but that does not always tell you what you need to submit for drawings, permit documentation, etc. It would be great to have a website that gives an example of what is an acceptable layout/design for each state. Hoping to hear any suggestions / methods that others use to determine what is required. Moderator Note: If there is significant interest in this topic, we'd be happy to open up a survey for areas that do require "full design" as an upfront submittal. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What is a building owner's responsibility to provide sprinkler system plans and calculations to new tenants and/or inspectors?
Is there any responsibility to provide these? Code sections would be appreciated, thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Has anyone come across a dual riser (dual-feed) sprinkler system in an office tower, with only a single inspector's test?
What is the proper method of testing each flow switch? In most cases, only the flow switch nearest the inspector's test will operate in a timely manner. Some inspectors will isolate and test, others believe the system should be tested under normal conditions with both control valves open. Is the deficiency the lack of a second test connection, or that the flow switch doesn't operate within 90 seconds (or even 5 minutes)? Alternatively, is there no deficiency at all? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe We are designing a clean agent system for electrical rooms located within a high-rise building. We are proposing having dedicated clean agent releasing control panels for the electrical rooms, and a separate building Fire Alarm Control Panel.
Is it mandatory to connect fire/smoke dampers (and other shutdown devices) in the electrical room with the clean agent releasing panel, or can these be connected to the building fire alarm system? Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe We are working on a mass notification system design. We have always called for any speaker/strobes in close proximity to the microphone to be shutoff during live announcements to prevent feedback.
Is there an actual recommended distance away that all speakers located within this distance should be shutoff? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe Does anyone have experience installing a heat detector in a cold environment (~ -40 degrees C or F)?
I'm thinking a rate-of-rise detector would probably be the right type based on what I've read but having problems finding a cut-sheet that supports that operating environment. Normally this type of space would get a dry sprinkler but some things have led to trying to think "outside the box" for this project. Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe Under NFPA 72 fire alarm manual pull stations are required on both sides of grouped openings over 40-feet in width and within 5-feet of each side of the grouped openings.
What about grouped loading bays or loading docks? Are manual pull stations required on each side of grouped overhead doors? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe Any good software resources out there for predicting fire alarm signal audibility across walls and doors based on their attenuation values and ambient sound pressure?
Editors Note: Another fire alarm question today, love it. Keep 'em coming! You can post any fire protection-related question using the "Submit Your Question" link below at any time. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe As a consultant, what level of detail do you go into for the line voltage (120v) fire alarm plans and wiring?
The line voltage is affected by loads / fuse sizes and affects the disconnect switch size. I'm wondering about the level of detail that an engineer should be showing versus leaving the sizing to the fire alarm and electrical contractors based on their specific system layout requirements. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe We have an auditorium project with a walkway that is constructed beside the seating area at the first and second levels. The second level has been provided with beam-type smoke detectors. There is a suspended ceiling below the walkway which is approximately 6-feet (2 m) from the wall. Do we need smoke detectors below this suspended ceiling? The design currently has smoke detectors only inside ceiling void spaces below the walkway - is this in compliance with NFPA 72?
The fire alarm contractor is arguing that if a fire originates at the floor level below this walkway, it will be easily detected by the beam detector at the second level due to the smoke buoyancy. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Have a four-story project that is under 2015 IBC and NFPA 101. NFPA 101, for fully-sprinklered buildings with accessible floor levels (floors 2-4 included) - designates the entire floor level as accessible and an area of refuge. Reference NFPA 101 7.2.12 and NFPA 72 24.10.
Along with that designation includes a requirement for a two-way communication system generally next to the elevator bank for the building. There's not much detail out of NFPA 101, and I'm finding very few people are familiar with these systems. Who typically specifies and provides details/locations on these systems? It is not tied into the fire alarm system - yet is related to life safety - so we're getting some feedback that these systems should be shown on fire alarm plans. However, the fire alarm subcontractors have nothing to do with these systems. Low voltage / specialty consultants are stating that the systems are code mandated and aren't looking to coordinate these locations with fire marshals and plan review. It's not a cost item and no one is pointing fingers - but I am trying to understand going forward where these systems are typically shown on plans and who should be specifying them? Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Are initiation devices (smoke detectors, manual pull stations, duct detectors) required to have individual labels on them showing the device address?
The project in question is military and is also subject to UFC requirements. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe NFPA 72 requires a battery test be run including removal of the main power supply, waiting the full-length standby time, then activating the fire alarm system for the full alarm time. After the alarm time, the battery voltage is required to be tested.
What is the pass/fail mark for the battery voltage? In theory, if the battery output still has 20.4 V, then the last appliance on a NAC circuit would still get a minimum of 16 V and everything still functions correctly. I just can't seem to find a code reference whether 20.4 V is the correct voltage to use (where a voltage reading below 20.4 V fails the battery). Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe I am a municipal fire inspector. We have a new high school, fully sprinklered, that has residential stoves in a classroom. These are protected with UL300A hoods.
Are these hoods required to be connected to the fire alarm? Common sense would indicate that if there was a fire hot enough to release the UL300A system, that the building occupants could be in danger and the fire alarms should activate, however, I cannot find a code reference for this. The architect is saying the stoves are residential so only residential requirements apply. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe Should return air duct smoke detectors associated with a fan system close only the associated damper and shutdown the fan or close all dampers on the system (including supply return spill and outside air)?
How should outside air and spill air fire smoke dampers be controlled? Should these to be controlled by fire alarm? Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe I'm working within a campus environment, and costs are something that always arise at some point during ITM conversations.
Does anyone have a great resource or tool to help to estimate a ballpark cost of ITM over a life of the building? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe I’m confused by the field of view intent of NFPA 72 for synchronization.
Do two adjacent rooms with a door between them each with strobe coverage require synchronization? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Question for AHJs and inspectors:
Do you occasionally see fire alarm strobes mounted on the ceiling that appear to be for a wall-mounted orientation (e.g. they are rectangular and have the word "FIRE" on the side)? I know some of these are actually for ceiling mounted applications but I've run across some that are wall-mounted only. I think the Wheelock brand might be an example? Stuff like this is hard to tell in the field for an existing building (with no documented cut sheets for what was submitted). Anyone have tips or tricks for this? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe What constitutes a "drop" on a fire alarm Class A circuit?
NFPA 72 12.3.8.1 (2016 Edition): "The outgoing and return circuit conductors shall be permitted in the same cable assembly, enclosure, or raceway only under the following conditions: (1) For a distance not to exceed 10 feet where the outgoing and return conductors enter or exit the initiating device, notification appliance, or control unit enclosures. (2) Single drops installed in the raceway to individual devices or appliances. (3) In a single room not exceeding 1000 sq ft in area, a drop installed in the raceway to multiple devices or appliances that does not include any emergency control function devices." For this project in question an appliance is located approximately 12 feet away from a device. The circuit runs from the device, out 12 feet horizontally, down a wall a few feet, then back up and back to the first device. In my opinion, the outgoing and return circuit exceeds 10 feet so it would not qualify as Class A wiring. However, the contractor is calling this a "single drop" to an individual appliance, so he feels it qualifies as exception (2) above. Is this considered a single drop if it's only serving an individual appliance? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Our common CRAC Units (Cooling, Refrigeration and A/C) for data centers only cool the air directly from the data center and back into the data center.
Do these need to be shutdown with the use of a total-flooding clean agent system? If the CRAC unit is only exchanging air within the same space then I'm not sure what harm it would do if it's running during or after clean agent discharge. I'm curious if I'm off the mark here, thanks! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe When an elevator does not have an elevator machine room, where should the fire alarm relays for the elevator be located?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Are there special requirements for fire alarm strobes on the exterior parts of the building (courtyards, etc)? Thinking that direct sunlight may interfere with the strobe.
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |