Under NFPA 72 fire alarm manual pull stations are required on both sides of grouped openings over 40-feet in width and within 5-feet of each side of the grouped openings.
What about grouped loading bays or loading docks? Are manual pull stations required on each side of grouped overhead doors? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Mitchell O
1/11/2021 09:12:40 am
From the handbook below (NFPA 72 [2016] 17.14.8.6), based on the handbook, I believe the answer to your question is 'no'. It states the objective is to provide pull stations within easy reach in the normal exit. I would say that loading docks are not normal exits (especially if finished floor is ~4ft above finished grade).
Reply
Todd E Wyatt
1/11/2021 09:20:11 am
The intent of the NFPA 72 is that manual fire alarm boxes be located within 5 feet of the "Exit doorway opening" at each Exit on each story. Overhead vertical doors are not permitted to be used as Exits since they are not "side-hinged swinging door, pivoted door, or balanced door" or (1) of the (9) exceptions to this requirement per 1010.1.2 Egress door types.
Reply
Jerry Clark
1/11/2021 09:22:26 am
No, overhead doors or horizontal sliding (such as hangar doors), are not considered code compliant exits and are not required to have manual pull stations.
Reply
Jesse
1/11/2021 10:10:48 am
No. They're not means of egress doors
Reply
sean
1/11/2021 11:07:07 am
it is not considered an exit and not required.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |