NFPA 13 (2016 Edition) Section 8.5.5.3 requires sprinklers to be installed underneath fixed obstructions over 4ft (48") in width and provides no further information on how that 4ft width is determined to be an obstruction. For most situations this is rather straightforward, but the open ended 4ft wide requirement leaves quite a few obstructions up to interpretation.
With that being said, how is it determined that an obstruction such as a duct, can be considered unobstructed if it is 40" wide by 6ft long, but if it is 48" wide by 3ft long, it is considered an obstruction? How is the obstruction rule only applied to the width of a piece of equipment and in turn is not applied to the length? Is there a ratio or rule of thumb that is widely used to determine whether an item hanging below the ceiling is considered to violate the 4ft rule? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Matthew King
11/26/2019 10:41:17 am
If you read later editions of code it defines 4 ft aide and less than 2ft above the floo . When you look at definitions of obstructions it become clearer as to continuous and non-continuous. In speaking with a local fire marshal, he said it the best: " if that sprinkler discharges and covers differently than it was designed to, and its 2 for more off the floor, the you need to put sprinklers under it." Assuming he is correct and the way I read code is correct, 4 ft a number that many n loop non-FPEs banter as an exception to fire usually isn't the issue.
Reply
Bruce Seiler
11/26/2019 01:24:40 pm
The annex of the standard states "the width of an object is the lesser of the two horizontal dimensions (with the length being the longer horizontal dimension)."
Reply
Alex H
11/26/2019 01:37:26 pm
In the NFPA 13 annex, section A.6.5.3.3 of the 2016 edition, it says, "The width of an object is the lesser of the two horizontal dimensions (with the length being the longer horizontal dimension). Sprinkler protection is not required under objects where the length is greater than 4 ft and the width is 4 ft or less."
Reply
Glenn
11/26/2019 04:51:41 pm
An addition to the above, it is A 8.6.5.3.3.
Reply
Bob A
3/30/2022 10:37:12 am
I don’t believe the original question about having multiple obstructions and the related gaps between them. To me this is a basic question about an obstruction wider than 4’ on the shortest side. I short the 4-FT obstruction rule applies outright.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |