About Pressure Reducing Valves for high pressure water supplies - I understand these need to be "indicating".
How can a PRV be an indicating type? What should I be looking for in inspections? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments
Dan Wilder
8/19/2020 09:22:20 am
The Pressure Reducing Valve would only need to be indicating if acts as a floor control valve in addition to being a pressure reducing. The larger valves like the ClaVal 90-21 or the ZW209FP is no different than a check valve and requires a shut off valve on the inlet side (and preferably the discharge side to avoid large drain downs). This is similar to the 2 checks of a backflow device that have the control valves on the inlet and outlet.
Reply
SK
8/26/2020 09:43:02 am
I don't think pressure reducing valve is to be indicative. These are just overpressure protection mechanism for downstream sections of the pumps, lines etc., These are set at predetermined pressure (say 175 psig if using Sch 40/Pipe with design pressure 175 psig) so whenever this demand increase where is potential overpressure is over 175 psig, Pressure Reducing Valve comes (PRV) into picture to protect the system, pops-ups/relieve excess pressure...otherwise in normal situation, stay with no use. The only requirement is to ensure upstream and downstream valve is kept open all the time.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |