When/why would an eccentric reducer ever be installed on a fire pump's suction side with the flat side on bottom?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
13 Comments
Wayne Ammons
11/18/2020 08:23:00 am
The purpose of an eccentric reducer on the suction side of a fire pump (when a size change is necessary) is to create a horizontal transfer of air/water into the pump. The orientation of the flat side depends on the direction of incoming water. If the water is incoming from below the pump, the flat side should be on top, if from above the pump, the flat side should be on the bottom, if there is a long horizontal run of water entering the pump the flat side should be on the top. You want as laminar a flow as possible entering the pump to help prevent future wear and tear.
Reply
Paul gowland
10/13/2021 02:38:28 pm
Hello Wayne I understand the eccentric reducer with flat end up under normal circumstances , however when supply comes from above main point of supply & back flow preventer is a floor above. So u are saying the eccentric reducer should be installed with the flat end down ? I did not see this in nfpa 20. Where is this noted per intall requirements? Thx!
Reply
gary lagnese
11/18/2020 10:10:30 am
Flat side is on top to prevent an air pocket that could cause the pump to cavtate.
Reply
Derek Gaston
11/18/2020 10:14:45 am
Hi Gary!
Reply
gary lagnese
11/18/2020 01:07:51 pm
Hi Derek!!!
Craig Vesely
11/18/2020 10:21:06 am
The flat side of the eccentric reducer is to have the flat side of the fitting on the top to prevent an air pocket from forming. Refer to Figure A.6.3.1(a) in the 2019 edition of NFPA 20.
Reply
Franck
11/18/2020 10:35:13 am
Wayne is right
Reply
gary lagnese
11/18/2020 10:51:20 am
Could not a concentric then be used>
Glenn Berger
11/18/2020 11:01:00 am
Flat on bottom is typically used on steam systems.
Reply
Franck
11/18/2020 11:04:26 am
Not if you want the flow to be as laminar as possible.
Reply
Wayne Ammons
11/18/2020 11:18:05 am
Replying to Gary Lagnese
Reply
gary lagnese
11/18/2020 01:12:17 pm
Wayne, I was only asking in reference to a vertical supply feeding the pump.
Franck
11/18/2020 11:12:30 am
You can also add to this list of reliability items the elbow at the intake on the horizontal plane...
Reply