When is the auto ball-drip required on the hookup (dry) side of the check valve for a Fire Department Connection?
In areas prone to freezing, there is the FDC, then a dry portion of pipe, then the check valve. If the check valve is located higher than the FDC (as is typical for our FDCs near risers), can't the connection itself drain the dry portion? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Wayne Ammons
1/31/2020 08:01:17 am
This is just to state what you probably already know, in order to comply with Section 8.17.2.1 and Figure 8.17.2.1 the automatic ball drip is required.
Reply
Franck
1/31/2020 10:17:11 am
Another possibility (if accepted) in your case and if you have caps, is to drill a small hole in the caps to allow any possible water trapped to drain.
Reply
Ryan D
1/31/2020 11:26:36 am
Another aspect that gets overlooked with this requirement is when a Stortz type connection is used. If the check valve leaks then the area behind the cap can become pressurized and create a hazardous situation for anyone needing to remove the cap. The ball drip alleviates this hazard as well.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |