What is the residual pressure and flow require for both public and private fire hydrants?
Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
franck
8/28/2020 10:38:35 am
For public, I don’t know minimum requirements in the US.
Reply
8/28/2020 10:50:46 am
Required Private Fire Hydrants shall be capable of discharging 1000gpm @ 20psi minimum as per IBC & NFPA 1 & 101.
Reply
Sheikh
8/28/2020 11:50:39 am
Can you please prove the reference of IBC, NFPA 1 and 101?
Reply
sean
8/28/2020 02:15:34 pm
I do not use NFPA 1 or 101 as often I will concentrate on the ICC model codes.
SK
8/28/2020 12:26:17 pm
Residual pressure and flow requirement are dependent for which client, Country, AHJ or occupancy working for?
Reply
sean
8/28/2020 02:16:52 pm
NFPA 13 does not influence hydrant design the fire code (IFC, NFPA 1) and NFPA 24 do.
Reply
Franck
8/31/2020 03:51:14 am
My understanding is that NFPA 13 requirements are for minimum flow demand (manual firefighting) considering that the entire facility is adequately protected by sprinklers.
Reply