Do underground gate valves for fire main water supplies have to be monitored and supervised?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Randy
1/20/2020 09:33:37 am
Not necessarily. See NFPA 24-2019 Section 6.7.2
Reply
Franck
1/20/2020 11:48:09 am
But many AHJs request it for private facilities, in particular Insurance Companies.
Reply
Jim Abernathy
5/20/2021 10:00:38 am
I have four underground 8 inch valves with valve boxes. How do I supervise these valves?
Reply
Joe Meyer
5/20/2021 10:05:32 am
Usually two options - chain and lock the valves, or run tamper switches from fire alarm out to the valves for electronic supervision. The requirements very much depend on the enforceable local codes.
Reply