We have a project where transformers are located on the periphery within a building's ground floor. There are 14 transformers within a single room. The life safety consultant has recommended for us to provide deluge system protection.
Is it required to provide a deluge valve for each transformer, or combine three or four transformers per valve? Also, how should sprinkler flow demand - is it calculated by each nozzle, or should we consider the entire transformer area for protection? Under NFPA 15 we have assumed 0.25 gpm/sqft (or 10.1 lmin/sqm). Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
GLENN BERGER
11/9/2020 10:25:13 am
Need additional information prior to responding!
Reply
Mike
11/9/2020 10:25:18 am
You can protect multiple transformers as long as adjacent systems that may be actuated are calculated simultaneously.
Reply
Justin Milne
11/9/2020 10:56:19 am
Is this a military, proprietary, or industrial job? Depending upon this, answers could be different.
Reply
Dan Wilder
11/9/2020 11:20:03 am
Are these transformers just the incoming SES and distribution equipment? I've had "Less Flammable Liquid Insulated Transformers" within buildings that were only protected by OH2 (overhead only) and curbing for containment (the building code dictates limits for the actual volume of liquid able to be within the building). Having this many within a room utilizing a deluge system would be a containment nightmare and depending on arrangement, would be better handled by individual valves per unit vs. having to combine multiple zones for simultaneous activation.
Reply
Franck
11/9/2020 12:05:29 pm
As already indicated, it all depends on the size of your transformers.
Reply
SK
11/11/2020 10:05:38 am
As long as cumulative demand of all transfer together should not exceed over 2500 gpm, you can cover multiple transformers. This is maximum allowed limited which can be supplied from single deluge valve.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |