I have a question on the difference between Fire Pumps vs. Sprinkler Booster pumps test header connections.
In NFPA 20 (2007 Edition) they speak of a test header connection to verify fire pump capacity via either a 3-way or 5-way connection depending on pump capacity. I have a test header with a flow meter installed and I am aware that test header connection is required for a "FIRE PUMPS". My question .. does this also apply to " Sprinkler Booster Pumps"? They are also under NFPA 20 but little mention is made. Should a test header be installed at all? Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
14 Comments
FIREPE25
10/9/2020 10:05:08 am
Can you enlighten me on what the difference between a fire pump and a "sprinkler booster pump" is?
Reply
JAMES
10/9/2020 10:21:23 am
I'm with you on this one - I'm not familiar with a "Sprinkler Booster Pump" but only Fire Pumps.
Reply
Colin Lusher
10/9/2020 10:20:40 am
Same question/comment as FIREPE25
Reply
Jonathan Joseph
10/9/2020 10:21:36 am
I'm guessing no standpipes and booster pump is used to meet sprinkler demand and simply be tested through a main drain to meet your required residual pressure at the base of the riser.
Reply
Chris
10/9/2020 10:24:45 am
I wonder if the poster is talking about a jockey pump?
Reply
DT
10/9/2020 10:29:01 am
I do not have the 2007 edition of NFPA 20 on hand, but perhaps the reference to a "booster pump" is actually a jockey or pressure maintenance pump which do not require test headers.
Reply
Franck
10/9/2020 10:53:05 am
A booster pump is definitely a fire pump and need to be tested from 0 to 150 % of its rated capacity.
Reply
Alex
4/28/2021 06:52:17 am
Thank you for the clarification as this is a NYC application.
Reply
Jonathan Joseph
10/9/2020 12:02:08 pm
I think booster pumps gets confused with fire pumps. The booster pump term and language is being written off in NFPA slowly.
Reply
Mike L
10/9/2020 04:04:23 pm
The poster may be inquiring about a NYC installation. Here in the Big Apple, we have different terminology for pumps given their arrangement.
Reply
Franck
10/10/2020 02:02:26 am
To Mike
Reply
Vincent Boves
10/10/2020 11:01:49 am
I agree with Mike L. New York City has it's own definitions. A fire pump services standpipe, not to be confused with a sprinkler booster pump which supplies sprinklers. Keep in mind that it's the same pump. But if you call it a Fire Pump it requires 2 independent 6" water supplies and the booster pump only requires one water supply. This labeling only works on low rise buildings, once you have a standpipe connected then you need two water supplies.
Reply
Alex
4/28/2021 06:53:12 am
Thanks for the clarification as this is a NYC application. 3/3/2021 02:52:43 pm
Fire pumps are used to boost the water pressure in sprinkler and standpipe systems and to deliver the required amount of water (Figure 3.5). This is necessary when the system is fed by a non-pressurized water tank, or when the water supply feeding the system has inadequate pressure.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |