NFPA 1 Section 13.2.2.2, a Class I standpipe is not required in buildings less than three stories or less than 50-ft high above grade.
If we have a huge industrial complex or storage occupancy of 60,000 square meters (645,000 sqft), should we not require a standpipe system if it is only one floor above grade with a total height of 40-feet? Looks strange to me. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Wayne Ammons
5/22/2020 07:34:55 am
You will probably need class I standpipe outlets being that it is a storage occupancy. See below from NFPA 1, 2015 Edition:
Reply
Craig Vesely
5/22/2020 10:40:51 am
To build upon Wayne's comment, if the jurisdiction where the facility is located uses the International Fire Code (IFC), the rules are slightly different. Section 3206.8 within the 2015 IFC states, "Where exit passageways are required by the International Building Code for egress, a Class I standpipe system shall be provided in accordance with Section 905."
Reply
Anthony Brown
5/22/2020 11:59:12 am
It is very important to check first with the AHJ seeing that not all locations follow NFPA 1 or the IFC.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |