Got a question regarding sprinkler protection above hung ceilings. NFPA-13 states that sprinkler protection is NOT required above hung ceilings if the area above has non-combustibles even with small openings in the ceiling.
However, I seem to recall a requirement that if there are large openings in the hung ceiling, sprinklers are required above the ceiling, but only for a certain distance in from the edge of the opening. Thoughts on what section provides that distance? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Randy
11/27/2019 10:03:40 am
If you have large gaps, it may be a cloud ceiling. Check those requirements.
Reply
zack
9/30/2020 07:50:29 am
Wooden rafter , the space between each others is 26 cm, i have sprinklers above them
Reply
Matt
11/27/2019 10:12:45 am
Sounds like you're thinking of "Extension of sprinkler system above drop ceiling" - check out 8.15.23.3, and by association, Figure A8.15.23.3
Reply
NK
11/27/2019 10:31:58 am
For sprinklers above ceilings with noncombustible construction:
Reply
Franck
11/27/2019 01:05:05 pm
Maybe you are thinking of the paragraph with open gratings (8.5.5.3.4 and annex in the 2016 Edition), which states that sprinklers should be provided below open gratings and should be provided with shields, Then there is a requirement for the position of the shield. The purpose of that is that the heat will go through the openings and collect first above the open gratings, therefore, sprinklers are required above the « ceilings with a lot of holes » as the sprinklers located below the ceiling will not operate quickly. But because of possible obstruction to the sprinkler discharge pattern from the open gratings’ sprinklers are also required underneath. And a shield is mandatory to avoid water cooling of the fusible element from the operating sprinklers above.
Reply
Franck
11/27/2019 01:09:10 pm
This means that it is the other way round compared to your question.
Reply
Richard
11/18/2022 02:37:11 pm
Alterations to an existing shell tenant space. Is it permissible to leave existing upright sprinklers in non-combustible space above new ceiling? All new pendant sprinklers are on return bends and uprights removed, four existing uprights are not accessible due to elevation issues. Can they be leftF
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |