I have a new highrise building with a water storage tank/room for the fire sprinkler system. The entire room is the storage area.
Is sprinkler coverage required for this room? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
14 Comments
Thomas Reinhardt
6/2/2020 10:23:14 am
Yes
Reply
NFPA 13, 2019 1.3.2 Level of Protection. A building, where protected by an automatic sprinkler system installation, shall be provided with sprinklers in all areas except where specific sections of this standard permit the omission of sprinklers.
Reply
Mike M
6/2/2020 11:46:34 am
Agree with AB.
Reply
James Phifer
6/2/2020 10:58:18 am
From NFPA 20: 2016 edition:
Reply
Franck
6/2/2020 01:28:55 pm
If you have water tank + fire pump, you need to protect the room because of the fire pump. If the room only houses the water tank and it is of non combustible construction (no insulation), I don’t see any reason for fire protection
Reply
James Phifer
6/2/2020 01:53:45 pm
True. But the basic premise of NFPA 13 is to sprinkler the entire building, except where omissions are allowed. To my knowledge, there is no exception that would allow an omission in a water storage tank room.
Reply
Mike L
6/2/2020 03:59:59 pm
Building codes stipulate where Sprinkler systems are required. NFPA-13 stipulates how they are to be installed.
Reply
Jonathan Joseph
6/2/2020 04:29:35 pm
To define this topic.
Reply
Grant
6/3/2020 11:12:38 am
It's a room within the building that acts as a storage tank.
Reply
Mark H
6/2/2020 04:33:49 pm
I agree with comments above that you need sprinkler protection in the fire pump room or any room in a high rise with the exceptions noted. But if you are talking about a separate poured concrete reservoir built into the concrete foundation built to provide flooded suction to your fire pump with limited access (no door to a "room" just an inspection / service access panel above water level so a non combustible confined space) I would review with AHJ ?
Reply
Franck
6/3/2020 11:08:02 am
I don't see any requirement in NFPA 20, nor in NFPA 22, to provide sprinkler protection for the water tank.
Reply
10/26/2020 02:29:30 am
You are absolutely correct and thanks for giving information about bfrs respond men unconscious in water tank . I loved your blog and thanks for publishing this!! I am really happy to come across this exceptionally well written content. Thanks for sharing and look for more in future!!
Reply
2/18/2022 07:04:01 am
Take a look at cushion tanks if you're looking for a tank that's truly adaptable. Although they can contain a great deal of water, you can also take them with you! They may have a wacky name, but they do a fantastic job. The use of a pillow tank has a lot of advantages.
Reply
5/31/2023 09:37:12 pm
Ensuring proper sprinkler protection in water storage rooms is crucial for fire safety. This article provides useful insights and recommendations for maintaining an effective fire protection system. Thanks for sharing this valuable information
Reply