Have a situation I've never crossed before: we have a very small building that's getting expanded. Originally the sprinkler contractor gave two options for the general contractor to price their underground fire sprinkler service - (1) is to provide a 2-1/2" main, the other (2) is to provide fire barriers in certain areas with automatic door closers to allow the room design method be used, and bring in a 2" underground.
I completely recognize that small underground pipe is not good practice and limits the future potential of the building. We recommended a 4-inch underground, but the increased cost for tap fees and underground pricing added $10-15,000 to the job which the owner adamantly refused. We were given notice to proceed with 2-1/2" underground and thus provided a 2-1/2" riser and 2-1/2" mains. The GC gave a different direction for the underground and pulled 2" underground and is providing fire barriers and automatic door closers. We've recalculated using the room design method and everything still works with the 2" underground, but the 2-1/2" riser and 2-1/2" main is already ordered and on the way to the jobsite. Does NFPA 13 have any restriction against having a larger riser or main size than the underground? Because of the change in building construction, we only need a 2" riser and 2" main but will instead already have prefabricated 2-1/2" in both. My thought is to have a permanent placard clearly affixed to the riser showing the situation and clearly identify on as-builts the methodology used. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
15 Comments
Jesse
7/14/2020 10:09:50 am
You have a problem.
Reply
Dustin
7/14/2020 10:22:34 am
Please provide code reference.
Reply
Jonathan Sullivan
7/14/2020 10:28:34 am
Regarding provision "B)",13-16 24.1.3.2 (2) only adds the not smaller than the riser provision if the system is not hydraulically calculated.
Reply
TC Lambert
7/14/2020 10:32:06 am
Being curious, as I have come up against situations like this here and there, I looked at NFPA 13. This limitation on the UG pipe size being at least as large as the riser is only for pipe schedule systems. If it can be proved by hydraulic calcs that the system demands can be satisfied you should be fine. That being said, I don't like the small UG size either. Since the GC has stacked the deck against you, I would push for an ample safety factor to be included in those calcs.
Reply
SUBMITTER
7/14/2020 10:34:23 am
Section 24.1.3.2 (2) is saying that the underground is at least as large as the system riser. That's only for pipe schedule systems - this system is hydraulically calculated.
SUBMITTER
7/14/2020 10:41:10 am
I wouldn't sign/seal the drawing either - if it wasn't code allowed.
Reply
Rusty Scott
7/14/2020 10:15:49 am
I've seen this before with warehouse risers where 6" underground is provided but in order to make the calc's work, a 8" riser is used and then sometimes transitions back to 6" on the horizontal. This would be the difference in bumping up the branch lines over the gridded system which is $$$. So I believe it is allowed due to code not explicitly stating against it (at least I haven't seen a code against it, doesn't mean it's not there), I believe it's more or less just not considered best practice.
Reply
Jesse
7/14/2020 10:23:43 am
Your situation would be allowed, because of the 6" main. That's the minimum size allowed.
Reply
SUBMITTER
7/14/2020 10:35:02 am
Correct - no hydrants on the lead-in, hydraulically calculated, no domestic flow either.
Colin
7/14/2020 01:03:51 pm
Jesse, this is a hydraulically calculated system with no hydrants. Please provide the code reference where it states that the riser must be the same size as the underground. I believe that's only for pipe schedule systems. While its not "best practice", I'm not aware of a code prohibiting what the OP is asking.
Nic
7/14/2020 10:27:15 am
NFPA 13 2019ed 5.1.3.2 says the incoming fire main can be less than 6" if the incoming main is at least as large as the system riser. So currently you have a problem if your riser is 2-1/2" and incoming main is 2"
Reply
SUBMITTER
7/14/2020 10:36:33 am
Even the 2019 section you've referenced, though, is only fir pipe schedule systems.
Reply
Nic
7/14/2020 10:50:23 am
Ah good point. Not sure how I missed that. I don't see where you it says you can't do what you have planned then.
KN
7/14/2020 10:46:49 am
It's common around here to tap the city main with one size, and then to upsize the pipe after the water meter. For example, you could tap the city main with a 2" pipe and then after the meter, upsize the underground to 2½" pipe or 3" pipe (depending your system demand). This obviously has an effect on your hydraulics, but if you can figure out a way to make the calcs work, there technicially isnt any problem with this.
Reply
SUBMITTER
7/16/2020 07:34:29 am
KN - just out of curiosity - do the hydraulic calculations typically accurately reflect the loss through the water meter and smaller tap?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |