A project that has evidence storage will have a new fire sprinkler system. The storage is anticipated to be solid back-to-back shelves no more than about 8 feet in height, but will hold crime evidence which could and will likely include firearms. What sprinkler design density is required for this area?
Posted anonymously by a member for discussion. Discuss this | Subscribe.
2 Comments
JAMES
10/30/2018 10:53:41 am
NFPA 13 lists cartoned ammunition, small arms and shotguns as Class IV commodities in annex material (NFPA 13-2016 Table A.5.6.3 and A.5.6.3.4).
Reply
WES
10/30/2018 11:15:25 am
If it's any help, UFC 3-600-01 lists armories as Ordinary Hazard (Appendix B-1.2, latest 2016 edition) where storage doesn't exceed 12 feet. UFC uses Ordinary Hazard as 0.20 gpm / 2,500 sqft for wet systems with ceiling heights up to 30 feet (Table 9-3).
Reply