Is there a minimum distance clearance required or recommended from the fire sprinkler and the top of a stacked washer dryer in small closet?
What is the reason for the clearance needed? I heard that 4” is needed for the clearance rather than the standard 18” in a public area. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Dan Wilder
2/10/2021 07:48:21 am
13-19 - 9.5.5.4 - If the closet is less than 400 sq ft, a single sprinkler at the highest ceiling level is sufficient without regard to obstructions or minimum distance to the wall.
Reply
CJ Bonczyk
2/10/2021 09:19:58 am
Dan is on point with everything above. Additionally, this is an issue with ASRS units where sprinklers are a couple inches above the movable storage trays inside the units. The purpose of the 9.5.5.4 rule is basically that the sprinkler location and clearance is irrelevant because it will flood the compartment during activation. Oddly enough we have had an AHJ require concealed sprinklers a half inch above the cabinets of a wine storage cabinet, knowing the plate and deflector would not drop.
Reply
Dan Wilder
2/10/2021 02:29:27 pm
As pointed out by MLANTAINGE (thank you again), the closet is measured by VOLUME and not AREA.
Reply
Jesse
2/10/2021 09:19:37 am
Well Dan beat me to it. Agree with everything he wrote.
Reply
MLantaigne
2/10/2021 09:31:10 am
I agree with Dan, but just wanted to point out that the closet size is limited a volume of 400 cubic feet in NFPA 13.
Reply
Dan Wilder
2/10/2021 02:19:09 pm
Good catch...!
Reply
Franck
2/10/2021 10:50:15 am
Note also that the 18" clearance between the top of storage and sprinkler deflector is not required for storage against a wall (only for other storage within the room that may affect the sprinkler water distribution pattern).
Reply