Looking for an answer to a basic discussion point concerning sprinkler spacing. A pendent sprinkler is on a 10'-0" ceiling which is 4'-0" away (horizontally) from a sprinkler in a lower wide soffit, at 8'-0".
Based on the higher sprinkler being so close to the edge of the soffit, the soffit creates an obstruction for the higher sprinkler. However, the lower sprinkler should it activate will undoubtedly throw water to the floor space directly below the higher sprinkler, yet neither sprinkler will directly spray the other. Are these two sprinklers (one at a higher elevation and one at a lower elevation) required to be a minimum of 6-ft apart horizontally? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Mike L
5/8/2020 09:53:23 am
Refer to section 8.6.5.1 (b) or (c) (2016 edition)...or use the handy calculator provided on this website.
Reply
Jesse
5/8/2020 10:07:09 am
What's the width of the lower soffit?
Reply
The Guy With the Question
5/8/2020 10:08:32 am
Width of the lower soffit is 5-ft. More like a lower ceiling area than technically a short soffit.
Reply
Keith Heckler
5/8/2020 10:10:18 am
The answer is no, it is acceptable. Te rational for the 6 foot spacing with standard spray sprinklers is the cold solder effect. If closer than 6 feet, then spray from a sprinkler will discharge onto the adjacent sprinkler, thus keeping the response element cool. Since the soffit creates a discharge spray obstruction, the sprinkler under the soffit cannot be dampened by the higher positioned sprinkler.
Reply
Franck
5/8/2020 11:12:01 am
Keith is right
Reply
Anon
5/8/2020 11:56:07 am
I was asked this recently, and I agree with Keith and Franck. Although one sprinkler may spray under the other, there is no direct wetting, so it is acceptable. Full disclosure - I wasn't 100% sure until I read an NFSA informal interpretation that was consistent with this.
Reply
Ivonn
5/8/2020 09:38:13 pm
What figure you use to check if it is an obstruction?
Reply