A couple of questions about an electric vertical inline fire pump:
(1) Is it necessary to build a rated room around a fire pump that is located in a boiler room that is already 2-hour rated construction? (2) Is it required to have a concrete base poured below a vertical fire pump if we can bolt the pipe flange stand to a concrete floor? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Yes, it is necessary to build a separate rated enclosure around the fire pump. Looking at the 2019 edition of NFPA 20, Section 4.14.1.1.5 specifically notes that rooms containing fire pumps are to be free from storage, equipment, and penetrations not essential to the operation of the pump related components. Boiler equipment is not essential to operation of the pump and therefore may not be located within a fire pump room. The only exception to this is domestic water distribution equipment as identified under Section 4.14.1.1.6.
Reply
Glenn Berger
1/5/2021 09:21:08 am
Concur with Craig for the fire pump rating and what can be installed in the fire pump room.
Reply
Brian Gerdwagen FPE
1/5/2021 09:39:27 am
The answer for the rated room is good.
Reply
Todd E Wyatt
1/5/2021 11:06:57 am
SHORT ANSWER
Reply
Tony C
1/5/2021 11:20:38 am
I agree with Todd as the IBC/IFC would take precedence.
Reply
Franck
1/8/2021 10:00:34 am
Boilers represent an exposure to the fire pumps.
Reply
On similar topic if you can guide me, for fire pump rooms located in basement, accessed through a common corridor, is this arrangement accepted if we provided the required fire rating, is t ok to have other rooms access (like plantrooms, storages) through the same corridor coming from staircase to fire pump room door ?