I recently acquired a project where I'm replacing all sprinkler in a residential home. Apparently the original sprinkler heads were the OMEGA that were recalled some years ago on.
These specific heads had a K=factor of 3.9 and although I have found only one direct replacement with the 3.9 K=factor, they are not cheap! My question is what would be an alternative replacement to these k-3.9 Omegas, and would replacements need to be the same k-factor? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
James Phifer
12/23/2020 09:28:05 am
Found this in NFPA 13, 2016 edition. Hope it helps.
Reply
Kelsey
12/23/2020 10:33:00 am
Came here to say this as well. The 5% has been close enough for me in a few situations but not all, and then more investigation is needed. Good luck to you!
Reply
Dave L.
12/23/2020 10:39:00 am
I'm confident a current replacement can be found with similar or better performance characteristics (and maybe similar takeout), and they should be replaced. But respectfully, are you certain it is an Omega with 3.9K? I don't recall (no pun) a 3.9K recalled Omega sprinkler.
NK
12/23/2020 09:31:40 am
I've run into a similar situation. You either need to match the fire sprinkler characteristics or survey the existing system and run hydraulic calculations to make sure the calcs work with a different k-factor. It could definitely be worth some design time to save the cost of expensive sprinklers if you're replacing a large quantity of sprinklers.
Reply
Casey Milhorn
12/23/2020 09:43:11 am
Of course the correct thing to do if you using a different K factor is to recalculate the system. The issue will be the possible can of worms you are about to open by doing that. You don't know what it was originally designed to at the time (or maybe you do) and water supply could have deteriorated over time. You might be left with a system that doesn't work even with the original K factor heads. The K3.9s were during a time when some of the manufacturers were in a race to have a K factor for every different spacing and scenario. NFPA reigned them all in with standardized K factors thankfully. Even with the same K factor head, there is still a chance that the design parameters have changed for that particular head. All that being said, if the AHJ is reasonable, there should be no reason to use a little common sense and throw a 4.2K in there as a cost effective replacement. It should throw just as far, if not farther with almost the same pressure as the 3.9K. That's my two cents.
Reply
Franck
12/23/2020 09:55:38 am
I can’t answer from a regulation’s standpoint (not living in the US), but the answer from NK is technically correct.
Reply
Franck
12/23/2020 10:01:07 am
Information from Casey are also good technical advices.
Reply
Mark Fessenden
1/5/2021 12:26:04 pm
The Central R-1M was a 3.9 K residential pendent sprinkler. It's listed flow ratings ranged from 9 gpm at 12'x12' & 14'x14', 14 gpm at 16'x16' & 18'x18', and 16 gpm at 20'x20'. The face of fitting to finished ceiling distance was 1-1/16" Max to 7/16" min. Current 3.0 K res pendents have a reduced water demand at spacings 16'x16' or less. I am not aware of a currently listed residential sprinkler with a 3.0 K that is listed for 18'x18' or 20'x20'. If your original R-1M's are spaced at 18'x18' or 20'x20', you would need to reevaluate your calculations. If your spacing is 16'x16' or less, you can simply drop in the current 3.0 K. You will likely need an extension piece to make up the difference in take out.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |