My employer owns several properties in with 2 fire pumps that are discharging to the same loop. The pumps were there when we bought the buildings. In most cases there is one electric and one diesel, but in other cases there are two diesel fire pumps.
The power purveyor is not considered unreliable by any criteria. Is there anything you can think of that would prohibit me from decommissioning a redundant pump for the purpose of saving on maintenance costs? Each pump is 2000 gpm and the greatest demand on the loop is less than 3,000 gpm. The pumps are provided in parallel. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Scott
3/13/2020 10:04:00 am
There might be an insurance company requirement above the normal fire/building code requirements. I used to work for a large insurance company and once buildings got to a certain insurable value, they would require redundant pumps with separate power supplies.
Reply
Efi Sher
3/13/2020 10:10:43 am
2 diesel pumps doesn't make sense.
Reply
sean
3/13/2020 01:13:13 pm
you still get redundant pumps.
RJ
3/13/2020 10:14:13 am
The maintenance costs on your existing fire pump would be far less then you would spend if you would have to replace it. Penny wise and dollar foolish. ( Not calling anyone foolish, but that is how he saying goes.)
Reply
Joseph
3/13/2020 10:17:22 am
Consider consulting a maintenance and reliability professional to determine the availability and reliability of your system. Any reported failures or periods of unavailability could help derive the reliability of each pump. Note, consider including lead time for parts and repair personnel schedules in the periods of unavailability to calculate "operational availability". If the respective reliability calculations for each individual pump drops to 70%, having them in a redundant configuration still achieves a system reliability of 91% assuming the switch from one pump to the next is 100%. Compare the availability and reliability the owner desires against the cost of liability and cost of maintenance on the additional pump.
Reply
Jesse Cecil
3/13/2020 10:26:16 am
Undoubtedly an insurance requirement. If the properties were designated as High Protected Risk, there would most likely be 2 pumps, even two diesel pumps - though the more common arrangement is primary electric and secondary diesel.
Reply
3/13/2020 10:32:37 am
This is most likely an insurance company requirement.
Reply
Chris
3/13/2020 11:26:46 am
The pump is 2000gpm and the greatest demand in the system is 3000gpm?
Reply
Franck
3/13/2020 11:39:13 am
All the above comments are right
Reply
DTC
3/14/2020 06:23:30 pm
In addition to insurance I would say consult the AHJ in our area you are required to have redundant pumps if your pump is feeding multiple buildings.
Reply
Kevin Green
11/15/2020 03:10:44 am
If a sprinkler system is installed in a business premise must it be maintained or can it be redundant.