Is it permissible to consider the refill supply for a water storage tank when sizing the tank?
The supply would come in above 20 psi. Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Dave Branson
11/17/2020 10:13:59 am
Yep. This is basically a minima-maxima problem - the outs minus the ins.
Reply
Glenn Warga
11/17/2020 10:25:53 am
See Break Tank calculation formula. 20 psi must be maintained at selected refill rate.
Reply
Logan Nootbaar
1/17/2023 09:04:43 am
What is this formula
Reply
James Phifer
11/17/2020 10:54:24 am
From NFPA 22:
Reply
Fred
11/17/2020 05:59:36 pm
Are water tanks that meet required amount required to be autofilled or is manual filling permitted.
Reply
Franck
11/18/2020 04:51:41 am
For a break tank, automatic refill is mandatory (for obvious reasons).
Fred
11/18/2020 06:13:30 am
Franck, thanks great points. I think as per 14.1.8 a water level gauge of some sort should be provided on a regular tank as well.
Franck
11/18/2020 04:55:26 am
The only requirement when using a break tank is that the tank capacity is at least sized for a minimum duration of 15 minutes with the fire pump operating at 150 percent of rated capacity.
Reply
red
6/25/2021 09:37:43 am
How do you calculate the city water refill rate into the tank? Is there a program and or formula?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |