We have a dormitory project where, on the first floor, and entry lobby at the front entrance connects directly into a main corridor that runs the length of the dormitory. On either end of the corridor are exterior exits. There are also exit enclosures from the two upper levels that discharge to the exterior on both ends of the building. This project is under NFPA 101-2018 and is fully-sprinklered.
NFPA 101-2018 7.1.3.1 and 28.3.6 state the following: 7.1.3 Separation of Means of Egress. 7.1.3.1 Exit Access Corridors. Corridors used as exit access and serving an area having an occupant load exceeding 30 shall be separated from other parts of the building by walls having not less than a 1-hour fire resistance rating in accordance with Section 8.3, unless otherwise permitted by one of the following: (1) This requirement shall not apply to existing buildings, provided that the occupancy classification does not change. (2) This requirement shall not apply where otherwise provided in Chapters 11 through 43. Because this is a new dormitory, Chapter 28 also applies: 28.3.6 Corridors. 28.3.6.1 Walls. 28.3.6.1.1 Exit access corridor walls shall comply with 28.3.6.1.2 or 28.3.6.1.3. 28.3.6.1.2 In buildings not complying with 28.3.6.1.3, exit access corridor walls shall consist of fire barriers in accordance with Section 8.3 that have not less than a 1-hour fire resistance rating. 28.3.6.1.3 In buildings protected throughout by an approved, supervised automatic sprinkler system in accordance with 28.3.5, corridor walls shall have a minimum 1∕2-hour fire resistance rating. Our question is - is the lobby, by code, considered part of the corridor (and therefore need to be rated)? Two ways of looking at this - one is that the code is strictly only discussing requirements for the corridor and not a lobby. The other way of looking at it is that the lobby is acting as the corridor when it serves as part of the exit access for the building. Normally a 1/2-hour rating wouldn't make all that much of a difference, but there's storefront in the lobby space between an adjacent office and the lobby which would have a cost impact to the project. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Michael Major
2/11/2020 01:10:54 pm
I hope this helps.
Reply
Kelly
2/12/2020 09:54:01 am
Love how these LS questions are always super quiet on here...I feel like the crowd on this site is def skewed suppression.
Reply
James
2/13/2020 11:53:50 am
Very well said Kelly! Agreed entirely, especially on the "big picture" view on an overall code approach.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |