A 500 sqft rated liquid storage room is to be created within a fully-sprinklered 200,000 sqft warehouse. How many 55 gallon drums of Class IIIB liquid (flashpoint above 200 deg F) can be stored within this room? a. 18 containers b. 36 containers c. 87 containers d. 90 containers Solution | Posted 06/06/19
6 Comments
SR
6/5/2019 06:53:01 am
d. 90 containers
Reply
DW
6/5/2019 10:44:16 am
I agree, 90 containers.
Reply
Brenton
6/5/2019 10:10:32 pm
D. 90 containers
Reply
david boggs
6/6/2019 02:19:33 pm
The IBC and IFC are code requirements by many states and AHJs.
Reply
Steve
6/7/2019 07:16:02 am
Will the exam have questions like this even though NFPA 30 was removed from the required references?
Reply
Joe Meyer
6/7/2019 07:36:07 am
No, this was just me including this 2018 question incorrectly without vetting it first. I'll be sure to check all the others prior to posting.