A remote project site does not have any water utility available.
Under the latest edition of NFPA 22 (2018 Edition of Water Tanks for Private Fire Protection, Section 4.1.1), the "size... of tanks shall be determined by the required fire flow and duration for the attached fire protection system(s) and the pressures required." Is this implying that the site fire flow for firefighting operation should be included as part of the storage volume for the water storage tank? For this project the sprinkler system's required water supply would be about 40,000 gallons, while water storage for site fire flow would be well over 240,000 gallons under IFC fire flow or 140,000 gallons under NFPA 1142. Prior versions of NFPA 22 required "the size... of the tank shall be determined by conditions at each individual property after due consideration of all factors involved." Posted anonymously by a member for discussion. Discuss this | Subscribe
11 Comments
RJ
2/4/2019 12:54:13 pm
I have used the following to figure tank size. System Demand plus Hose Demand times Duration = Gallons (Tank Size).
Reply
James Phifer
2/4/2019 01:08:08 pm
The outside hose demand can be ignored unless the hoses come directly off the tank piping. see appendix below from NFPA 13.
Reply
David C
2/4/2019 04:51:11 pm
RJ & James are correct, one other point is it depends on what the tank is for.
Reply
JW
2/5/2019 09:25:02 am
If your tank serves fire hydrants then you need to consider site fire flow demand for tank capacity. I would explore NFPA 1142 Standard On Water Supplies For Suburban And Rural Fire Fighting. Depending on your site you may be able to propose a reduced site fire flow per NFPA 1142, if approved by the AHJ.
Reply
PETE
2/5/2019 12:13:43 pm
IFC and NFPA 1 both allow for up to a 75% reduced fire flow requirement for "fully sprinklered" buildings, as approved by the AHJ. Also, NFPA 1 §18.4.3.1 allows for decreases by the AHJ for rural areas where the development of full fire flow requirements is impractical. This provision is also in the IFC §B103.1. Also, In NPFA 1 (2012)§18.4.5.3 For a building with an approved fire sprinkler system, the fire flow demand and the fire sprinkler system demand shall not be required to be added together. The water supply shall be capable of delivering the larger of the individual demands. * On a personal note * The terms "fire flow" and "sprinkler demand" should not be confused or used interchangeably. Everything I've read in the codes makes distinctions between the two.
Reply
Ahmed
12/20/2023 01:59:44 pm
Thank you
Reply
Franck Orset
2/20/2019 11:20:38 am
Water demand for hydrant should be added to the water flow for the largest sprinkler system demand if the water supply is used for both the sprinkler systems and the hydrants.
Reply
4/15/2021 05:31:39 pm
I agree that the required fire flow should determine the size of the tank. Too small and you run into a problem. Too big and you'll pay too much money to fill it up.
Reply
Tom Kennedy
10/8/2021 08:10:45 am
If the underground tank is the only supply for the sprinkler system and there is a dry hydrant connected to the tank, would a hose demand need to be included in the sprinkler calculation?
Reply
James Phifer
10/11/2021 09:04:28 am
yes, I believe so per Annex A from the 2016 edition.
Reply
Tom Kennedy
10/11/2021 10:31:34 am
Thank you, James. A.11.1.5.2 is referring to sizing the tank (volume). My question is referring more to the sprinkler system hydraulic calculation, wondering if a 250gpm outside hose flow would need to be added to an ord. hazard sprinkler system hydraulic calculation. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |