Do sprinkler service entry sizes have a minimum mandated size for an NFPA 13 system?
If I do not have a hydrant on an incoming line and can prove hydraulically that a 3-inch service entry works, is that acceptable under 13 or only permissible in 13R or 13D projects? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Franck
4/21/2020 08:58:30 am
(To be confirmed by US resident, more used than I am to US requirements)
Reply
Jonathan Sullivan
4/21/2020 10:20:50 am
Franck - you are correct.
Reply
MIKE
4/21/2020 10:13:28 am
Refer to NFPA 24.
Reply
Jonathan Sullivan
4/21/2020 10:27:36 am
Mike - can you provide a section reference? I had thought that the Size of Fire Mains sections matched between the two standards.
Reply
Mike
4/21/2020 03:36:10 pm
My mistake. I can't find a reference but I remember it from somewhere or maybe it's just my imagination.
James Phifer
4/21/2020 10:39:37 am
Check Out NFPA 13 2016 ed. chapter 24 section 24.1.3
Reply
Thomas Jones III
4/21/2020 10:48:40 am
No minimum size requirements for incoming lines that I know of. However, if it is a combined domestic/fire line you do not have to include the domestic demand in your calculation if the line is 6" or larger.
Reply
Jonathan Sullivan
4/21/2020 10:54:52 am
I'm used to separate feeds for these services. When do you see combined used and how are these designed? NFPA 24 and local utility requirements from street into the building, and then tee off to domestic and fire services inside?
Reply
Pete D
4/21/2020 11:03:34 am
Don't forget to consider that you are designing for the current occupancy and all future occupancies, and material is not the largest contributor to cost.
Reply
Marc A Hyman
10/25/2022 11:05:31 am
Exactly. I am dealing with a situation now where i am completely renovating an old mixed-use property and the plans were drawn and approved in DC with 2" incoming service lines for both residential/commercial water and fire suppression.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |