I need to label some deflagration vents as "out-of-service" since they are not being maintained properly and are currently not needed from a code standpoint (as the use of the room has changed). We do not want to remove them as the room may be changed back one day depending on research needs.
Does anyone know if there is a code reference that points to the size of the letters or font type for an out-of-service-tag? In this case a tag is not practical since it needs to go on a flat panel. I know there are such requirements for exit and "no exit" signs, but I'm not aware of any code guidance for out-of-service signs. Thanks in advance for any feedback. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
sean
10/13/2020 10:35:50 am
The code says to maintain or remove.
Reply
Richard Mercer
10/13/2020 10:39:40 am
The IFC requires all non required fire protection systems to meet the respective installation and maintenance expectations, otherwise they would need to be removed. I'm not aware of code language that would allow labeling as out of service.
Reply
sean
10/13/2020 11:18:45 am
Similar language about maintaining mechanical systems is found in the property maint. code as well
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |