In regards to a dry-pipe system with a fire pump on the supply; is a jockey pump required on the wet portion between the pump and the dry-pipe valves?
I have to assume the answer is yes, since pressure needs to be maintained in this line if leaks develop over time. Please confirm/advise. Thanks in advance! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Mike ike
4/9/2020 10:13:33 am
Not nessasarily. I've designed monitor systems without a jp since the system was manual and pump would turn on from the pressure drop after the control valve is opened.
Reply
Franck
4/10/2020 04:48:30 am
That's weird
Reply
Pete D
4/9/2020 10:20:18 am
A jockey pump is a high pressure low capcity (flow) pump. The reason they're included is to make-up pressure that bleeds off of the private service main network without hammering the system with the full power of the fire pump in a no flow condition. Their necessity exists independently of the type of overhead system connected.
Reply
Franck
4/10/2020 04:40:35 am
Fully agree with that comment.
Reply
FIREPE25
4/9/2020 12:54:14 pm
In my opinion the best way to deal with a system in which you have a very small amount of wet pipe after the fire pump is to install an excess pressure pump. NFPA 20 does not require pressure maintenance pumps to be listed. An excess pressure pump utilizing a pressure switch will save you money. Also, Jockey Pumps on this arrangement have been known to short cycle. An excess pressure pump will alleviate this problem as well.
Reply
sean
4/9/2020 07:41:41 pm
a pressure maintenance pump is there more for longevity then anything else.
Reply
Mark
4/10/2020 02:10:05 pm
FOr that or a deluge valve header application I like the excess pressure pump option FirePE25 suggests. Albany pump makes one and could control start and stop with Potter PCS switch.
Reply
FIREPE25
4/10/2020 02:13:07 pm
Mark, good point about the deluge valve. Most of the projects we have done this on are large freezers with pre-action systems.
Reply
SK
5/19/2020 02:38:43 pm
Dear All,
Reply