I've heard that pressure reducing valves are not recommended and should be avoided on sprinkler or standpipe systems where possible. Has anyone had any experience or insight as to why this is?
Posted anonymously by a member for discussion. Discuss this | Subscribe.
8 Comments
Mike
11/21/2018 10:08:04 am
I'm curious where you heard this. Considering they are required to be listed there is practically no chance of failure when they are properly maintained and installed. In some instances, standpipes, their use is unavoidable.
Reply
Thomas Jones III
11/21/2018 10:16:04 am
On Thursday we received a call from a hospital because our competition was refilling a system and the PRV would not set. Additionally the PRV assembly was not installed per code so there was no bypass. At the end of the day there was something caught in the valve so flushing it fixed the problem. But the hospital and the competition had a very long frustrating night. So yes, they do fail. Install per code in case they do. (Two in parallel with control valves).
Reply
Mike
11/25/2018 02:01:41 pm
Sorry, that's not a failure A failure would be that if fails to regulate pressure.
Reply
11/21/2018 10:18:45 am
Pressure reducing valves or other mechanical appurtenances which are subject to mechanical failure are prohibited in main suction supplies to fire pumps.
Reply
Dave L.
11/21/2018 10:45:36 am
...for 1-1/2" outlets, correct?
Reply
11/21/2018 01:37:21 pm
PRV valves do fail in both the open and shut position. Most manufactures recommend a minor rebuild (rubber parts replacement) every 3 years for diaphragm style valves. For this reason if valves are to be installed to regulate a stand pipe system its best if there is a control valve on both sides of the PRV so the rebuild can be a smooth process.
Reply
Mike
11/25/2018 02:11:04 pm
If there is no bypass, what is the use of the downstream valve?
Reply
Nimal Tissa Wijetunga
11/22/2018 02:09:00 am
Recommend to identify the residual pressure to maintain below the maximum test pressure of the components and accordingly you may be able to calculate pressure loss on height of the building and pressure loss on friction of the components where you may be able find the height in relation the above and thereafter having another mechanical room where you can position another pump set with water tank.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |