Is a sprinkler ever not required in an electrical room? We typically provide sprinklers in all electrical rooms, but are being asked specifically if we can omit one on a project.
Posted anonymously by a member for discussion. Discuss this | Subscribe.
4 Comments
Diaa
11/8/2018 07:31:52 am
Sprinklers are required in Elec. based upon some conditions in NFPA 13 Clause No. 8.15.11.2
Reply
Barry Williams
7/21/2020 11:01:29 am
If electrical rooms do not meet the criteria for the installation of sprinklers as required in the IBC, Chapter 5, where in the code is the requirement for installing sprinklers in electrical equipment rooms?
Reply
RJ
11/8/2018 09:49:40 am
Ask the AHJ. They and the insurance agency have the final decision.
Reply
Scott Walter McBride
11/8/2018 10:19:10 am
The key is that ALL of the requirements are met that DIAA mentioned. Most electrical rooms become sudo storage rooms and would then have to be protected by sprinklers.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |