We have a small project (13,800 sqft total) which is a four-story, all residential apartment building, using mostly CPVC pipe. The system is under NFPA 13R.
The city supply is very poor, so we will have a fire pump that meets NFPA 20 (as is required by 13R). The pump is an 8-HP, 70 PSI at 75 GPM. Is a jockey pump necessary with such a small fire pump? Normally, for our large commercial NFPA 13 projects, a jockey pump is not even a discussion because we don't want the main fire pump (500 - 1,500 gpm) cycling on just to support system maintenance pressure. For such a small project with a significantly smaller fire pump, is there any harm in not providing a jockey pump? The question is not based on cost - the pump room is microscopic and we're already having trouble fitting in all the equipment and controllers as is. Appreciate you all - thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Peter
2/12/2021 09:08:31 am
A jockey pump is required under all installations except under a few scenarios when the fire pump is a positive displacement pump per NFPA 20, 2016: 4.26.7. The size of the pump is irrelevant.
Reply
OP
2/12/2021 09:11:43 am
Thank you Peter! Had always provided them, but didn't realize it was mandated as part of NFPA 20. Thanks for the standard reference.
Reply
matt
2/12/2021 09:39:33 am
I would disagree with peter. NFPA 20 4.26.1 specifically says that a pressure maintenance pump is one approved method - NOT required.
Reply
Peter
2/12/2021 11:06:29 am
Matt,
Reply
Matt
2/12/2021 11:20:25 am
I would recommend a jockey pump.
CJ Bonczyk
2/12/2021 10:18:54 am
NFPA 20 - A.4.26 Pressure maintenance (jockey or make-up) pumps should be used where it is desirable to maintain a uniform or relatively high pressure on the fire protection system. A domestic water pump in a dual-purpose water supply system can function as a means of maintaining pressure. A.4.26.2.1 The sizing of the pressure maintenance pump requires a thorough analysis of the type and size of system the pressure maintenance pump will serve.
Reply
Franck
2/12/2021 10:36:20 am
As a fire pump may start automatically upon pressure drop and normally does not stop when a higher pressure is obtained, you may have an issue if there is a pressure drop in your system (small leakage somewhere that slowly put the pressure down) that start your pump automatically if you start it upon a preset pressure in the system.
Reply
Mike
2/12/2021 12:38:09 pm
A jockey pump is only required where the fire pump is started by pressure actuation. Some systems may use pumps but may not require constant pressurization as is the case with manually operated foam systems.
Reply
Phil W
2/14/2021 12:08:35 pm
Where you do have a large system/s that does need a pressure maintenance pump, I would even consider providing two (one as back up) given the chaos that can happen if the duty jockey pump fails (fire pumps constantly starting, alarms being raised, building evacuations.....) We often offer a contingency spare at least
Reply
Onur
2/15/2021 07:07:18 am
Hello to everyone,
Reply
Oscar Relucio
10/23/2022 05:20:17 am
My comments below consider logic and practicality more than invoking the code.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |