My fire sprinkler system was poorly designed. Static fire water pressure is constantly at or above the relief valve rating. This causes the valves to constantly discharge. I can't rebuild the fire system.
Can I put two valves in parallel or in series to reduce pressure? Would that invalidate the system? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Dan Wilder
5/20/2020 08:17:29 am
Is the system working pressure above 175 PSI or is it below 175 but the relief valve continues to leak?
Reply
Jonathan Sullivan
5/20/2020 08:34:12 am
Awesome explanation Dan. Also this was addressed from an installation standard perspective here:
Reply
Casey Milhorn
5/20/2020 04:15:23 pm
Yup, Dan nailed it. Surprisingly many of the sprinklers, valves, fittings, and couplings are rated above 175 psi nowadays, compared to when I started in the biz. You might already be okay, as Dan mentioned, to just simply swap out the pressure relief valve to a higher pressure. Next I would talk to the City and see what they can do to help out if the first option doesn't work. Pressure regulating/reducing valves would be my last resort. They add inspection and testing costs to you annually, are prone to failure, and could lead to early repair/replacement costs.
Reply
Stephen Aikey
5/20/2020 12:50:39 pm
Not sure I would be so quick to blame the Sprinkler Design! Sounds like the relief valve is working as designed. Would like more information as to where the high pressure supply is coming from?
Reply
Pete D
5/20/2020 08:15:31 pm
If the sprinkler design required 175 psi at a 40 ft roof elevation, it would need to have roughly 192 psi at ground level. If you had a 185 psi rated relief valve it would constantly leak. You need to look at the sprinkler hydraulic calcs to see what is required at the pump discharge, and look at the safety margin. If the additional pressure is needed in your installation, a higher rated relief valve can be installed on each riser. If the added pressure isn't needed, it may be as simple as dialing back the off theeshold on your jockey pump controller to fix all systems leaking.
Reply