Please can someone give some information regarding the filling speed of a empty pipeline to a sprinkler line?
In my case there was water hammer in a 6” line, The 16” firewater line was under 175 psi pressure and the opening time was 9 seconds. Is 3 feet per second more realistic? Or is there a NFPA standard that addresses this? Thanks in advance for your support! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
FIREPE25
6/11/2020 10:22:29 am
My understanding of water hammer is that it is more of a problem associated with when valves are shut and water stops flowing abruptly. That is why NFPA 13 requires slow close valves. It is also why fire hydrants are closed very slowly to ensure the underground pipe is not damage.
Reply
Jose BOHORQUEZ
6/11/2020 12:20:34 pm
Es correcto la informacion , para complementar el golpe de ariete también de produce por la micrexplosiones que se dan al activarse las unidades de bombeo.
Reply
MIGUEL ANGEL D ADARIO
6/11/2020 11:21:38 am
In my experience, it would be advisable to make the pipe very slow and complete, releasing as much air as possible at the opposite end, mainly from the highest points. Once this is done, it must be pressurized, (for example, by means of the jockey pump).
Reply
Jeremy James
6/12/2020 08:16:49 am
Contractor: Is this on a dry system? Either way, cracking the valve and letting the system fill slowly for a few minutes will decrease the hammer. We typically use earthquake bracing, required or not, throughout the feed main piping, where we have a 90 and turn directions.
Reply
Bruce Verhei
6/15/2020 04:09:59 pm
Are you concerned with the water system outside your building or only your system?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |