NFPA 25 requires a legible Hydraulic Information Sign.
How do I replace a missing Hydraulic Placard (or calculation plate/card) on an existing system? And what if there isn't original design information available? I'm curious to see how others are addressing this deficiency. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
25 Comments
Matthew King
3/2/2020 10:14:16 am
The insurer usually wants/photos the placard. Find out who the previous owners were and track down the insurer
Reply
Jonathan Griffin
3/2/2020 10:14:19 am
Your choices:
Reply
Dan Wilder
3/2/2020 10:23:24 am
We follow this method as well but in the absence of original design info, we will preface that if the design does not calculate (for a flow test deficiency or an occupancy that does not work with the installed sprinkler system), we will not provide the placard.
Reply
NK
3/2/2020 10:52:13 am
Do you use the most current edition of NFPA 13 or do you use the edition of NFPA 13 that was used at the time of the original design/installation?
Jeremy James
3/2/2020 10:26:02 am
As a contractor, we often run into this issue after an inspection. Typically, we would approach the owner for as-builts, but they are rarely onsite (if there's no placard, you probably won't find a print). We would offer the service of a designer to reverse layout the system with a field survey and then perform a calculation for the placards. This can become pricey for the customer, depending on the structure and if pipe is exposed or above ceilings.
Reply
Rz
3/2/2020 11:22:51 am
Since you only need the require gpm and psi at the base of the riser can’t you perform the hydraulic calculation without a flow test and save the customer some monies
Reply
Imran Mahmood
5/5/2022 12:53:03 am
We have the original calculation sheet but placard is missing.
Reply
Jonathan Joseph
3/2/2020 11:17:04 am
If you cant track down the prints through the company that installed, or AHJ.
Reply
Peter
3/2/2020 03:00:39 pm
Why do you need to perform a flow test? You're not providing a curve. NFPA 25, 2014 and later requires that the system have a hydraulic data plate on it if it is pipe scheduled or hydraulically calculated and that plate be secure and legible. NFPA 13, 2013 25.5.2 doesn't require flow test info either. The hydraulic data plate dictates the requirements of the system. Additionally, most hydraulic data plate signs don't have a spot for the water flow test information, I know the ones we use don't. The general information sign has information about the water flow test.
Reply
Jonathan Joseph
3/2/2020 04:28:15 pm
I don't think you are getting the original question and concern.
Peter
3/2/2020 04:39:09 pm
Jonathan,
Reply
Jonathan Joseph
3/2/2020 06:39:51 pm
Correct LOL
Reply
Dan Wilder
3/3/2020 07:29:26 am
@NK
Reply
Mike
3/5/2020 01:58:01 am
How or why would you need to provide a hydraulic calc plate if the system was pipe scheduled?
Reply
Peter
3/5/2020 06:22:22 am
Starting with the 2014 edition of NFPA 25. If the system is pipe scheduled, there needs to be a hydraulic information sign that says it is pipe scheduled.
Reply
Ramon
5/21/2020 11:16:14 pm
You can do a survey and find out if it is a pipe schedule system or not... Just by looking the pipe...
antonio
8/16/2021 02:40:45 pm
so, can we assume if the building is pre 2014 a Hydraulic name plate is not necessary ?
Mike Magwire Sr.
8/18/2021 11:05:47 am
I am interested in your reply to Antonio's recent question as to the
Reply
Peter
8/18/2021 11:34:17 am
For some reason I can't "reply' to Antonio's comment as the button doesn't appear.
Reply
12/17/2021 01:31:03 pm
Hello - I have a related question with a healthcare client (hospital) that has Sprinkler Systems installed form the early 1970's. They keep receiving Deficiencies for not having a Hydraulic Name Plate on the sprinkler system.
Naveed
10/12/2021 05:28:40 pm
Related question: We have some old buildings with domestic water line coming and then splitting into fire and potable water lines. Now we are bringing in separate fire water and need to know flow rate and pressure required for the sprinkler line. No as-built, placard is available. How can we find the required info? Is there a simple way to do it?
Reply
We are missing the placard for the Sprinkler System Control Valve riser. Every attempt has been made to contact and locate paperwork. Everything is negative. New Insurance carrier requiring we replace placard. What would it cost and who would I go through tp have this completed?
Reply
Joe Meyer
10/12/2022 10:28:01 am
Hi Mark,
Reply
Peter
10/12/2022 02:43:35 pm
If you can't locate sprinkler drawings of the existing system you'll need to have the sprinkler system re-calculated. This can be relatively easy or incredibly complex depending upon a multitude of factors. For example, a 3 story residential building has a relatively simple calculation procedure, but it may mean making access holes if there is no attic space to see the direction of the pipe, pipe type, pipe size, etc.
Reply
Bruce Powelson
12/30/2022 05:45:57 pm
The system was installed 2011. I have a print of the approved plans from Department of Building Micro fiche signed off with approval stamps and hydraulic information on the face sheet. I have contacted the installing contractor by using their license number. Our insurance Company wants a Hydraulic Plate. The original contractor wants $450.00 for the plate, which seems a little like black mail. Are there any alternatives.