I have a question that a architect brought up to me. He is saying that on a highrise (11 stories) it is a fire code requirement to have floor control valves on both stairwells. I cannot find anything that states this in any of the NFPA books. The square foot of each floor is small and is NOT separated into zones.
Does an 11-story high-rise require floor control valves on both stairwells? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Mike L
1/14/2020 07:54:17 am
Kind of sounds like the architect is confusing some code requirements.
Reply
Mln3d
1/14/2020 09:44:50 am
Unless it is a justificational adopted code requirement. Some AHJ’s require floor controls to alternate that way if you need to drain down the system it doesn’t completely impair the system. i.e. if you only had floor controls on one stand pipe and drained a floor down.
Reply
Thomas Jones
1/14/2020 10:06:51 am
It isn't an FM building or Marriot correct? Marriot has their own fire code that requires a control valve in each stairwell.
Reply
Anon.
1/14/2020 10:32:37 am
Some AHJ's require this. Last I checked, City of Seattle for example has such a redundancy requirement, but in hydraulic calcs, one cannot take advantage of both supplies simultaneously.
Reply
Diaaeldin Mostafa DM
1/14/2020 11:05:05 am
As per NFPA13 , Only one sprinkler riser with floor control valve per 52,000 ft2 . If NFPA 101 is asking for stand pipes so it shall be provided inside firemen stair or smoke stop lobby or fire fighting lobby
Reply
RY
1/14/2020 11:43:49 am
How high is your building? It is not an NFPA requirement. It is in the IBC... in PA we follow IBC 2015 and it is on page 58. 403.3.1 Number of Sprinkler Risers and Systems Design...
Reply
ML
1/14/2020 12:02:49 pm
Yes, heard of this too.
Reply
Thomas Reinhardt
1/14/2020 01:50:28 pm
If you use the International Fire Code Section 903.4.3 states that Approved supervised indicating valves shall be provided at point of connection to the riser on each floor in high-rise buildings.(2012 edition) This reference makes no reference to both stairwells. Mr.Mostafa is correct about square footage.
Reply
Brian Gerdwagen FPE
1/14/2020 03:56:00 pm
As stated, buildings over 420 feet to the highest occupied floor must have two risers. Each of these risers will supply alternate floors and the standpipe valves in the stair. One riser will supply all the even floors, the other all the odd floors. This way if an entire standpipe is shut down, only half the building will be out of service.
Reply
Moshe
9/30/2022 07:39:19 am
According to this code will it be a problem if 2 floors in a row are the same ?
Reply
Jess L.
1/15/2020 12:08:04 pm
Check your building code.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |