Without the context of a specific project or problem, when would you recommend creating a separate, detached fire pump house versus a fire pump room inside a building?
Is is purely a risk perspective? Do you recommend fire pump houses only when a pump is feeding multiple buildings, or a campus? I've only had a few projects that used a fire pump house, and it has generally been in retrofit situations or when the pump is next to a water storage tank. In either case the pump house overall cost more than it would have should the fire pump room been within the building (even despite the simple construction of the pump house). Just curious on getting another perspective. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
PETEY PABLO
6/4/2019 10:49:05 am
When it's infeasible or difficult to obtain a fire-rated separation for pump room walls, you can use a detached pump house at 50 ft. from the building instead. NFPA 20 §4.12.1.1.2.
Reply
Joe Meyer
6/5/2019 06:20:16 am
Agreed Pete(y). Diesel driven pumps' host of exhaust and ventilation requirements make a pump house an attractive option.
Reply
SK
9/5/2019 11:10:42 pm
Hi Petey,