Is sprinkler protection required for laundry rooms with electric dryers?
This project is in New York City specifically. Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments
Dan Wilder
8/20/2020 08:53:47 am
In each of the 13, 13D, 13R Standards (2019) under "Equipment Closets:
Reply
Mike L
8/20/2020 09:01:26 am
Yes, per section 903.2.11.13, laundry drying rooms with more than 2 dryers are required to be sprinklered. No distinction is given on the type of dryer (electric or gas).
Reply
Doan
4/26/2022 03:15:31 pm
The fire inspector requests
Reply
Glenn Berger
8/20/2020 10:46:49 am
If your building is sprinklered, then yes this room will also require sprinklers.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |