On recent inspections I've seen many installations where an automatic ball drip is not provided anywhere on the pipe connection between the fire department connection and the check valve that serves the fire department connection. Is there an exception I'm missing or isn't that automatic ball drip always required?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
Dan
6/6/2019 10:08:52 am
Refer to NFPA 13, A.8.17.2.6. It is required in areas subject to freezing. In areas not subject to freezing, where water would be trapped between the FDC check valve and the system, an auxiliary drain is needed.
Reply
Scott McCormick
6/6/2019 11:58:13 am
I am in a Local Enforcing Agency and was told by a sprinkler contractor that an Storz FDC doesn't need a ball-drip because its only needed on an FDC with a clapper, i do disagree because if the check valve doesn't hold the Storz FDC pipe could have water in it. My other comment is how contractor have put the ball-drip at the check valve when the check valve is not at the lowest point.
Reply
6/7/2019 09:08:56 am
Removing a Storz connection under pressure could be hazardous to the mechanic/fireperson.
Reply
Frank Herrick
6/7/2019 10:22:37 am
FDC ball drip is always required, regardless of Stortz or NH connection.
Reply
6/7/2019 10:49:03 am
As far as the question, personally I think it would depend on the ball drips design and manufacturers intent.
Reply
Jrob
6/7/2019 12:19:49 pm
I dont think I've ever seen a ball drip that you can install in the vertical position. I suppose if it was spring loaded it would work, but never seen one.
Reply
Pierre Lemieux
7/14/2020 06:23:13 pm
Most ball check models are required to be installed in the horizontal position (not all). You will usually see a 1/2" street elbow installed on the inlet side of the check making the ball check operate in a horizontal position.
Reply
Brian Cook
1/18/2021 07:36:30 am
“Yes” That is what makes them work properly, if they were installed in a Vertical position the ball would go to the bottom and block the flow
Reply
Jack G
6/12/2023 09:23:52 pm
A spring loaded ball drip can mount either vertical or horizontally. A normal plunger type, horizontally.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |