Does the proximity of a residence and the number of windows on that residence make a difference in which system type is used (between NFPA 13, 13R, or 13D)? What are the restrictions that would impact the system type?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
Wayne Ammons
10/29/2019 07:38:19 am
Interesting question, check out one of Joe's recent blog posts:
Reply
Pari
10/29/2019 11:36:48 am
in our jurisdiction any single home greater than 10,000 S/F, fire sprinkler design shall be per NFPA13R and attached or detached garage greater than 750 S/F shall be design per NFPA 13.
Reply
10/30/2019 02:44:17 pm
13-D is limited to 1 and 2 family dwellings. Water supply has to supply just two sprinkler for 10 minutes.
Reply