I am looking at a sprinkler relocation-job were food is to be packaged. They are installing a drop ceiling above the packaging equipment.
I am having a hard time finding a concealed sprinkler head to spec out that has a metal temperature element and a rubber dust cover that is suitable for an ordinary hazard space. The VK538 jumped to mind but they do not offer a rubber gasket for the plate. I just found the TY5521 that says it comes with a rubber dust seal. Do FDA-grade facilities require dust cover gaskets? Does adding a dust cover ring to a escutcheon de-list the product? Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
RJ
2/21/2020 10:07:12 am
Have you looked at Reliable G-5 Heads? They have a metal temperature element and have gaskets.
Reply
Salvatore Izzo
2/21/2020 10:09:04 am
Check out the Bulletin 034 for the Reliable G5 standard response concealed sprinkler with gasket cover plate. It is cULus Listed for both standard response and quick response, It utilizes a solder link thermal element.
Reply
Dan Wilder
2/21/2020 10:15:00 am
Escutcheons are listed with the sprinkler so, in the case of the TY5521, the listing actually changes from QR to SR when used. You cannot just add the escutcheon to another sprinkler.
Reply
Pete D
2/23/2020 08:20:51 am
I have designed for multiple USDA facilities. The requirement for ceilings above food processing is for corrosion resistance for washdown areas, which in the case of packaging likely applies. The sanitization requirements are in 9 CFR. You can use polyester or 316 SS semi-recessed sprinklers in these areas. All exposed pipe should be 304 or 316 SS, all rods SS cold rolled with threaded ends.
Reply
2/25/2020 11:30:58 am
Take caution if compliance with FM Global approval is required. The Reliable G5-80F does have FM approval but our experience has been that FM has additional restrictions on it use including use only in light hazard occupancies, noncombustible construction, no flammable liquids, limited plastic commodities, noncombustible contents, etc. It is also only approved by FM as standard response. FM also requires the sealing gaskets to be physically inspected on an annual basis, by running a metal hook around the gasket perimeter to ensure that the gasket is not adhered to the ceiling.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |