There's likely to be a wide perspective on the value of engineer-provided sprinkler layouts on plans that delegate the full-design to the fire sprinkler contractor. Do you feel they provide benefit? Take the poll and comment below.
[Don't see the poll below? Click here.]
7 Comments
PBJ
3/26/2019 10:10:15 am
It really depends on the complexity of the project.
Reply
Dan Wilder
3/26/2019 10:36:40 am
When the Engineer follows the joint position as detailed in the below link. Even going a step further for correct main locations along approved structural members is OK because that typically reserves the space for our trade (not one truss down the middle of a 35K warehouse when a grid system is obvious). I'll even take a sprinkler layout (pendents in a ceiling) provided it's been coordinated at the design level (not into lights/HVAC/security/emergency lighting...). Beyond that, let the design tech (contractor) use NFPA as needed to provide a code compliant system.
Reply
Pari
3/26/2019 10:37:48 am
Especially on government projects , engineering design required before go to bid for contractor.
Reply
Kelly
3/26/2019 10:49:20 am
I think engineer sprinkler layouts are important where you have a certain aesthetic you're trying to achieve (read: the architect wants you to make them look better), or if you are doing a renovation/retrofit project and must coordinate ceiling tile spaces for the contractor to get a decent bid. Otherwise, let the contractor do the design. They are better at that level of detail and have far more experience in the field than 99% of engineers. Typically I will show and size the mains so that we can get a field of tighter bids, but I don't want to dictate too much or get in the way of a more efficient design than I could have come up with.
Reply
Mike
3/26/2019 01:40:51 pm
I find little value from large FPE firms the design fire sprinkler systems because they may know the technicalities of NFPA standards and manufacturers recommendations but they generally do not provide enough detail to qualify as a shop drawing level of design. It still falls and the fire sprinkler contractor to fix it.
Reply
Chris
3/29/2019 07:29:07 pm
They make the estimator's job much easier, but more often than not, fall to the wayside because of bad reputation. As a contractor, I've worked off of a couple of engineer-designed systems. In some cases. their way is the only way and it's a copy-paste sort of job. This has been due to--as mentioned above--architectural needs, or sometimes structural steel demands. In others, the sprinklers are spotted just to get a print out and (to a contractor) it's a garbage design that can be significantly improved upon.
Reply
Patrick Drumm
4/17/2019 08:49:50 am
I'd be interested in what the results would be for a similar poll by area / region. I'm always curious if Engineer Sprinkler layouts are any better or worse in respect to other areas within the US. I particularly work in the Northeast.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |