We are looking at a boat storage facility in the northeast. The facility is 42-ft high storing fiberglass boats. It's unheated. The owner doesn't want in rack sprinklers, nor does he want a fire pump.
What would be the fire sprinkler design criteria for this type of facility? Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments
Wayne Ammons
3/11/2020 08:12:50 am
You should get a fire protection engineer involved with this if you have not already. Check out NFPA 303, Fire Protection Standard for Marinas and Boatyards for additional section references:
Reply
Jon Sullivan
3/11/2020 10:10:56 am
I'd also recommend a review of your applicable Building and Fire Codes to see if you require sprinklers based on building construction, area, and occupancy. IFC considers indoor dry boat storage as S-1.
Reply
Jesse Cecil
3/11/2020 11:12:33 am
At best it will be protecting Group-A. I think the owner's desire to avoid a pump is right up there with my niece's desire to get a rainbow unicorn for her birthday unless your extant water supply is outstanding
Reply
Michael
3/11/2020 12:15:06 pm
This sounds like insurance underwriting responsibility.
Reply
Jesse Cecil
3/12/2020 11:44:31 am
I spent 13 years as an insurance loss control engineer. The building owner may want to query his / her insurer to see what their underwriting requirements are. If their loss control guy deems the system inadequate, the owner's premiums will be astronomical.
Reply
Bruce Verhei
3/16/2020 12:45:17 pm
It is appropriate to communicate directly with the fire department to. This site needs a preplan. A base document (.pdf) is often of great assistance.
Reply
Mike
5/10/2023 08:52:02 am
i am working on a 135' high boat storage building with 8 tiers of boats. the Fire Marshall has mentioned foam. what would the sprinkler design/requirements for a building like this be?
Reply
Smith
1/25/2024 11:33:11 am
What happened?
Reply
David T Williams, FPE
1/25/2024 09:53:50 am
Whew... I think about all that I have learned since 2005, when we completed my one and only heated rack storage boat building (maybe four tiers high). I remember one of the main issues with the State of WI was whether a boat was a motorized vehicle that needed garage ventilation (whether fueled or not). I couldn't find my records on what I did for design, although they recently replaced the boilers. At that point we didn't have that much guidance on what to install for fire protection, so I think it was just a OH2 design. Now... what did the contractor provide? it was definitely reviewed by WI Code folks (Madison so they were tough).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |